dannyb

Hi

I have just tested the Zs on my ring final circuit...

i got the readings 0.25, 0.32, 0.47 and 0.52

there are more but the readings were basically between 0.25 and 0.52

Ze is 0.11 and r1+r2 is 0.35

i get the same readings either at the front or the back of the socket so with the test leads or the test lead with the 3 pin plug on the end.

i understand the parallel paths or worn accesories may effect the reading.

the lowest reading was the first socket in the ring and the highest was the furthest part of the ring...... ( have i just answered my own question there?)

oh and the highest readings are not spurs cz i have checked that too.

for some reason i was expecting the same sort of reading at all the sockets......

can anyone enlighten me please

Danny
 
your Zs readings will increase as you get further from the CU to the mid point, whicich will be the highest reading,unlike R1+R2 because the latter are cross connected when reading.
 
Thanks F for that! i had a sneaky suspicion as u can see from the original post.

ok the next thing is.... if Zs = r1+r2 +Ze

then my zs should be 0.46

my highest reading was 0.52

and parallel paths only bring the zs down not take it up
 
There are a number of factors that can influenece the Zs reading such as meter accuracy, cable connections, test lead resistance, socket outlet contact condition etc etc.

TBH, I wouldn't worry about the reading you have as it sounds fine to me.
 
thanks lenny


just the question rises . i know all the connections are tight and i tested from the back of the socket as well as the front. i just cant explain how the Zs can be higher than calculated.

the tester is calibrated as of january 11 the leads are mint condition

i knew the reading was ok i just had to ask cz i cannot explain it....

if it was less than calculated id have said yeah parallel paths but tiz not the case

Danny
 
Ze readings can vary that why I was always taught to test Ze and PFC twice one straight after the other..... Surprising the differences in value you see
 
yeah thats todo with the Cycle.

all good feedback thanks everyone...

i can have my niceid assesment relaxed now....TOMORROW!!!!
 
your only 0,06 out, id be fine with that, ive seen much bigger differences, like then man said, so many external influences effect test results, right down to the make up of the cable when ur talking such small values as 0.06
 

Reply to Zs testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi folks. Im a RECI contractor based in Co Sligo, Ireland . I was doing erroneous testing on a domestic board which gave me readings between 90V-...
Replies
14
Views
2K
I've just finished an installation on a large outhouse around 50 meters from the main property, but I'm having issues with unusually high Zs...
Replies
11
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock