hi guys,
Hoping for a little advice.
Been working on a property this week and have been having trouble getting zs readings as it trips the rcd on a 17th edition cu.
Property is pme. I've tried testing idividual circuits one by one and completely disconnecting all the others but it still trips. It doesn't seem to matter what circuit is tested it trips on every one.
I've checked absolutely everything and all tests leading up are fine. Zs tests however trip rcd.
I've done a ramp test on rcd to check that and it's fine.
I've got a feeling it's a Dno issue but they have now confirmed there are no faults on the line. Anyone had similar issues.
Thanks in advance
 
You know what they say Tel, 3rd time lucky
 
I'm with tel, if it's happening on every circuit it sounds like you're running a standard Zs test rather than a no-trip.

Also, make/model dependent, make sure you are using 3-leads if your tester requires it. When I first got my tester, I was running a no-trip Zs, but only with 2 leads having been used to a Megger. Turns out my Metrel needs 3 leads to do the no-trip.
 
the 1552/3 meggers use 3 leads. it's only the 1700 series that can do no trip with 2 leads.
 
Definately no trip guys.
Megger 1730. Two settings hi and low and I'm on low
Yes tried it on next doors circuits. Worked fine. It's the first time it's tripped rcd on a zs test with me.
 
on testing zs on the megger 1730, it is possible you have a problem tester I self.
when testing 3 low using plug or leads their should not have a problem
I had same problem many years back with 1502 sent it back megger sent me a new one .
did you turn the dial to off position and start again.
 
Try clamping the tails to see what leakage is there before you test as even on No Trip your still injecting 15mA into the cct so you may have a leakage which puts the RCD above its Ramp value just a thought!
 
Were there any suspicious IR readings? Particularly in the N-E department?



The question was no how many leads did you connect, but whether it is a two or three lead test? These are different things!

Ditto IR fault (neutral-earth), can cause RCD to trip on Zs 3 lead test.
 
Ditto IR fault (neutral-earth), can cause RCD to trip on Zs 3 lead test.

Exactly, and you'd hope that anyone who is carrying out these tests would actually understand what they are testing and the basic principle of how the tester performs the test.

I don't understand the mindset of just pushing the test button and writing the number down, what does it really achieve?
 
Try clamping the tails to see what leakage is there before you test as even on No Trip your still injecting 15mA into the cct so you may have a leakage which puts the RCD above its Ramp value just a thought!

Odd, I thought the megger used 200mA with DC blocking on the low current test?
 
Definately no trip guys.
Megger 1730. Two settings hi and low and I'm on low
Yes tried it on next doors circuits. Worked fine. It's the first time it's tripped rcd on a zs test with me.

My 1730 has three loop impedance functions on the L-PE setting:

3Lo (3 wire non tripping loop for RCD protective circuits (Zs))
2Hi (2 wire high current loop measurements (Ze/PFC))
2Lo (2 wire non tripping loop for RCD protective circuits (Zs)
 

Reply to Zs tripping rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
284
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
733
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock