ZS
Discuss ZS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
R
rapier
Evening Guys
Just 2nd fixed a barn conversion at work.
We are using a 3 phase board as the suppliers provided 3 phase.
So on all the circuits we used rcbo's at c type i dont know why my boss choose c types.
So when i came to test the installation the results are fine but are over on max zs but not by a million miles away.
So are these fine as there protected on a rcbo or should i tell my boss to convert to b type rcbo's.
Thanks guys
Evening Guys
Thanks guys
hi there
i seem to recall where the ZS cannot be met the installation of a rcd was required to give additional protection in order to meet the required disconnection time of the protective device where this CANNOT be achieved. his would explain the rcbo
I would look again at the ZS as did you take into account the R! and R2 correction factors for temperatue Guidance not no3 page 107 appendix B
I have done 2391 testing but have not come across this in the course was in the old guidance notes just had a look shows we cannot always kep up with the changes
cheers
Reply to ZS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...