Evening Guys

Just 2nd fixed a barn conversion at work.

We are using a 3 phase board as the suppliers provided 3 phase.

So on all the circuits we used rcbo's at c type i dont know why my boss choose c types.

So when i came to test the installation the results are fine but are over on max zs but not by a million miles away.

So are these fine as there protected on a rcbo or should i tell my boss to convert to b type rcbo's.

Thanks guys
 
Evening Guys

Just 2nd fixed a barn conversion at work.

We are using a 3 phase board as the suppliers provided 3 phase.

So on all the circuits we used rcbo's at c type i dont know why my boss choose c types.

So when i came to test the installation the results are fine but are over on max zs but not by a million miles away.

So are these fine as there protected on a rcbo or should i tell my boss to convert to b type rcbo's.

Thanks guys


hi there

i seem to recall where the ZS cannot be met the installation of a rcd was required to give additional protection in order to meet the required disconnection time of the protective device where this CANNOT be achieved. his would explain the rcbo

I would look again at the ZS as did you take into account the R! and R2 correction factors for temperatue Guidance not no3 page 107 appendix B
I have done 2391 testing but have not come across this in the course was in the old guidance notes just had a look shows we cannot always kep up with the changes

cheers
 

Reply to ZS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
501
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
931
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
260
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
964

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock