  1. Rocboni

    KLEIN Toolbag for sale

    KLEIN tool bag. Never used. Comes with led light. £70??? Open to reasonable offers Post available
  2. Rocboni

    UFH8 or UFH8N system

    I recently wired a heating system with a UFH8 manifold and an unvented cylinder.... easy. Well it threw up a few problems. Initially I had the time clock live feeding the UFH16, ugh zone valve connected to the valve connection and fired the boiler with the volt free on the pcb LS and LR. Circ...
  3. Rocboni

    Sky + & TV first Fix

    Hi all, Looking for some advice on first fix for sky and freesat TV, I've quoted a WF100 shotgun and a single to both bedrooms and lounge, plan was to run all shotguns to external point for Sky to terminate into LNB and fit amp and digital aerial for the 3 freesat points. Terminated in each...
  4. Rocboni

    Transformer testing

    Hi All, So i was asked to look at at large 3 phase to 120V transformer around 85kVA - it was tripping the MCB instantly (it never used to) I insulation resistance tested the primary windings to earth - >2000ohms I continuity tested the windings and got 0.46 ohms per winding, they were all...
  5. Rocboni

    Outdoor building/stable

    Hi all, Pricing for a supply to a 25x 10M steel frame shed around 100M from a bungalow, one section is going to be partitioned to create a stable area. Is there any requirement for a 300ma S type RCD?, I wouldn’t really class it as agriculture. Only 2 double sockets well away from the stable...
  6. Rocboni

    Load regulated feeder control

    Heres one for you automation gurus. I'm looking to control the speed of a rotary feeder or conveyor that feeds a hammer mill on a farm. In order to achieve maximum efficiency the feeder needs to be regulated via the load of the hammer mill. The 55Kw motor on the hammer will be started using a...
  7. Rocboni

    New supply to factory

    Just wondering what people thoughts are on obtaining a supply to a part of a local mill where I am now a maintenance engineer. The existing installation is terrible with many switch fuses that have been added over the years, the oldest part is from 1946. The total supply capacity in question is...
  8. Rocboni

    Closed loop Sensor monitoring

    Hello, How are closed loop sensors like the below and monitored integrated into a control system, isolation switches/switch amplifiers? These are typically used on explosion panels where when they blow off it snaps the cable or ceramic plate causing an open circuit. (I’m Prepared for the...
  9. Rocboni

    Fairford synergy soft start unit

    Looking at using a fairford synergy soft start unit as below to start a 45kw motor, just wondering what it means by connected in line, I’m presuming they mean star but can see how the motor would run correctly being 400/690v rated...
  10. Rocboni

    Ade optima compact bleeping

    Hi, I’ve been asked to look at a ADE optima compact plus as the zone 1 light is activating and it beeps everytime the PIR as activated I.e when someone walks Infront of it even when the system isn’t armed? You can press reset and the light goes off but as soon as it activates again it comes...
  11. Rocboni

    Bargain fuses On ebay

    Just won these on eBay for £1.20 feel a bit guilty to be honest, not sure if I'm going to take them 253199553457
  12. Rocboni

    Filling out EIC tick sheet

    Query when filling out EIC for an additional circuit, When filling out an EIC for additional circuit, Is the tick sheet applicable to that circuit only or is is talking about the installation as a whole? For example where it states Cables correctly supported throughout their run obviously this...
  13. Rocboni

    45kw motor and generator problem

    Hi all, Got a bit of a problem with a new generator when starting a 60hp motor. It's a 250kva generator with a 125A mounted plug, the plug is protected by a C125 A Merlin gerin c120h MCB with combined 300mA RCD, the motor starts fine but when it changes over to delta it trips the 125A mcb (I...
  14. Rocboni

    Frost protection on combi boiler

    Quick hypothetical question, Combi boiler in garage with frost stat and pipe stat on return pipe, two zone valves for upstairs and downstairs, does the frost stat have to open one of the valves or just fire the boiler? Do they have a bypass valve?
  15. Rocboni

    Serrated washers on steel conduit

    Whats the opinion in serrated washers with galv steel conduit? I was always taught at college to have one in between coupler and accessory and coupler and trunking, wether being used as the cpc or a separate cpc. I was at a job today where they are installing a trunking/conduit system but are...
  16. Rocboni

    Lighting trunking

    So workshop with perimeter 75x 75 galv trunking, with overhead lighting trunking suspended from rod with hangers, lighting trunking is quite a bit higher than the perimeter trunking, how do you link the two? Would you use an internal bend and flange it down onto the trunking at either end? Or...
  17. Rocboni

    Earthing and bonding

    Copied this from trainee section to see if I can get an answer, it is talked about a lot on the forum but reading through the old posts I can't determine whether I'm right or wrong. What I'm looking to understand is sub main earthing conductors. Is what I am saying right? So a sub main to an...
  18. Rocboni

    ERBAUER ERT576SDS 36V sds drill

    ERBAUER ERT576SDS 2.8KG 36V 2.0AH LI-ION SDS PLUS CORDLESS DRILL Excellent drill with great reviews on screwfix, never been used or out of box, with all original packaging. Fast charger, 2 x 36v 2.0Ah batteries, depth stop looking for £235 Postage £10
  19. Rocboni

    HNC electrical engineering

    In 3rd year you are not at college for a basically a year until the fica preparation night classes, I have not worked out dates to confirm it is feasible but I am considering doing the HNC electrical engineering in this 3rd year, I sure the night classes won't conflict with the examination dates...
  20. Rocboni

    Right or wrong?

    Recently our family friends had a supply installed in there winter yard (travellers/showmen), being a trainee and having just covered special locations section 708 at college,I was interested to see how it Was done. Supply is as follows. 3 phase TNS supply 25mm tails to 63A 4 pole switch fuse...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock