I have a small power washer with a two-wire cord and GFCI plug. My outdoor and garage receptacles are on a "house GFCI" circuit, wired in series to one GFCI receptacle. I tried to use the power washer and the plug GFCI would instantly trip when plugged-in and instantly re-trip when reset. I have gone through several replacement connectors but each only last long enough for the current project. The pressure washer's GFCI would trip each time and I would need to replace it each time. It did this when connected either to the outside GFCI receptacle or to an inside, non-GFCI receptacle. I took apart the plug and it is a 2 wire GFCI on the pressure washer side. I want to convert the pressure washer GFCI to a regular plug. Regular plug is 3 wire. If I connect the hot and common to just the 2 bladed poles of the new plug, there will not be a ground?. Is this safe if it is plugged into an external house GFCI outlet, if it even works at all?

Thanks in advance for any advice.
 

Attachments

  • plug.jpg
    776 KB · Views: 4
If the supplied GFCI plug on the power washer is tripping, that would normally be because the current flowing in the hot wire is different from the current flowing in the neutral (return). That would happen when there's a leakage current flowing to ground within the power washer. If you have changed the GFCI and it carries on happening, I suspect your washer is faulty.

Don't change the plug because of the tripping - that would bypass a safety measure that the manufacturers are obliged to fit to the product to protect users. Removing it could make the situation dangerous. The tripping is telling you there is a problem in the washer that needs to be investigated!
 

Reply to iRoyce Pressure Washer - Going from a GFCI plug to a normal 2 plug. in the Electrical Appliances Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock