Discuss Log cabin supplies in the UK Electrical Forum area at ElectriciansForums.net
Multicore 90°C Armoured Thermosetting Insulated Cables​
Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,
Voltage:400V
Load:44.34kW / 80A
Length:190m
Method of Installation direct in ground or in ducting in ground
Cable Size:35mm²
Voltage:400V
Load:44.34kW / 80A
Length:190m
Cable Size:35mm²
For volt drop 35.0 in undersized.
That calculated from Cleveland cables.
@westward10 point is that is when you have a balanced 3-phase load so only the losses in L1-L3 are a factor as N current is near-zero, if you have just one cabin drawing 80A then you get double the drop (L & N losses) so I'm guessing that is the 8% mention above, but I have not actually checked it.
But as @James points out 80A seems a lot for a wooden cabin! If heater cooker, and shower all on at once maybe, but allowing a bit of diversity, and/or maybe a priority unit cooker/shower would drop the peak load and make the overall drop acceptable.
Going up from 35mm to meet drop is going to be expensive. However, it seems 80A draw for a log cabin is quite high, more than many flats have as a supply!
So before sizing the cable to meed VD for 80A on a single phase of the three, are you sure that it really is needing that much?
You don't need to meet VD at the supply OCPD current (though you can find issues with disconnection times if not careful there), nor even at the max permitted by the sum of load OCPDs, but you do need to meet it at all realistic levels of usage. Can you tell us the loads and assumptions you made for the 80A figure?
Reply to Log cabin supplies in the UK Electrical Forum area at ElectriciansForums.net