bonding

  1. Q

    Max continuity reading for bonding

    Good evening I was always taught the gas and water bonds should have a continuity ideally with a maximum of 0.05 ohms, is this a exact maximum or a rule of thumb and if it was higher than this what coding would we give it? I had a look through the codebreakers booklet but could not bit see an...
  2. cliffed

    Sub main & bonding conductors

    Installing Swa 35MM 4 c,to new school block. This supply will come of a MPB,nearby,to me the supply to this MPB does not comply. Concern once again are the size of the bonding conductors realative to the the Main REC supply. The drawing we have,have no input on this, it’s a Tncs system,& earth...
  3. E

    UK Main Bonding Dilema

    Hi guys, just looking for a few thoughts on this one. This is a pretty big property with the gas meter situated in a small outhouse. There is no power in the the outhouse. The supply pipework comes out of the ground in copper into the meter. Then exits the meter in plastic and goes below...
  4. A

    Unable to locate water meter/stopcock

    Hello all, just want your opinion on something. I'm currently testing retail stores and I cannot locate the water meter/stopcock. There is a 10mn earth that goes into the ceiling from MET. I have went round with my R2 lead and am getting 0.03-0.04 in kitchen, toilet etc. Like I said no sign of...
  5. D

    UK Static/Tingle from shower/towel rad.

    Hi, working in a property a couple of years old. Earthing System is a TN-C-S. Customer’s daughter/wife have both complained about receiving a “slight tingle/static sensation” when using the shower in only one of the bathrooms (when touching the shower/or towel rad). I’ve checked the incoming...
  6. T

    Bonding question

    Alright folks, Looking for a bit of advice with supplementary bonding - pictures attached for context. Bit of background - I'm in the process of repairing some metal bollards: I decided the best option was to rip out the old guts which comprised of some old fluorescents complete with all the...
  7. Ruairi Hansen

    Gas bonding

    Hi guys just wondering what peoples thought is on this. I was out looking at a job today and noticed the main gas pipe is not bonded at the meter but has a 10mm earth at the boiler is this a code c2, c3 or nothing?
  8. W

    Moving equipotential bonding, Minor works>

    Hi, I was having an disagreement with a work mate, a client has been told that their bonding (gas) is in the wrong place, (it is). This is the only job we have to do there and obviously after moving it and carrying out the required continuity tests, would you issue a minor works certificate...
  9. L

    UK Static bonding of flour pipes

    Hi All Looking for advice if anybody’s got any knowledge on static electricity. been asked to bond flour pipes at work Do you take it back to the nearest panel or take it to a earth spike ?
  10. K

    Earthing and Bonding question

    I need someone to enlighten me about Earthing and Bonding. We've just completed the construction of four Fabricated Steel Bay Structures with a total of 354 Stansions 102 Beams, all connected to the Porlins, the place is to be used to seat 120,000 persons. I am not in doubt of the importance...
  11. T

    Main bonding to water question

    Hi folks, Just wanted to check and see if bonding is required in this situation: There's no bond to water pipework, bond to gas all present and correct There is a piece of plastic pipe at the point where the water enters the building, probably around 100mm in length There is then a mix of...
  12. GBDamo

    2.5mm or 4mm SWA armour bonding

    Armour not CPC. By the letter of the regs 2.5mm is acceptable as the DB offers both mehanical and corrosion protection. Just seems a bit puny on a 10mm SWA, what about a much larger cable? Can some of the boffins explain why 2.5mm is deemed acceptable. Cheers
  13. A

    Earthing and bonding new build

    Hi guys bit of advice needed to save me some time and money. Earthing and bonding required in new build property. 10mm earth to be ran to gas meter to clip to gas pipe that will enter property. This gas pipe then goes to a combi boiler where I will bond all pipes at combi to the gas pipe (gas...
  14. Mark42

    Bonding metallic back boxes. Best practice?

    Something about the way this box is bonded feels wrong. I prefer the box to remain bonded even with the accessory removed. Is this method compliant? What do others think? (Ignore missing grommet) (Taylor Wimpey new build)
  15. L

    Gas Bonding Conductor in 20mm conduit

    The scenario, Property has no bonding to gas meter. There is a 4mm T+E radial from the DB to an outside socket which is located 300mm from the gas meter (external meter). The 4mm T+E is housed in 20mm plastic conduit running along the external wall. To prevent things looking a complete mess...
  16. driverman

    Additional supplementary bonding

    Ok new house. New install cert issued. However, no supplementary bonding that I can see and accessible . There is a 10mm earth wire connected above the water stop cock point of entry under the kitchen sink. However, no cross bonding to the hot pipe. According to install cert the cross bonding...
  17. B

    Bonding Cast Iron Pipe

    Hello. The toilet is connected into a cast iron waste/soil pipe O.D. 150mm. Apparently, this is an extraneous conductive part and is thus supposed to have a main protective bonding conductor connected back to the MET. There is a bonding clamp for 150mm O.D. pipes available. However, the pipe...
  18. Maxine

    Earth bonding for meters

    Hi, I am just after some advice. I am having new meters fitted and been told they need to be earth bonded? I've attached a photo as my friend thinks this has been done but I need to know before I book an electrician, so any help is appreciated, thank you
  19. newfutile

    supplementary bonding

    we are allowed to omit supplementary bonding on the 3 conditions (rcd, disconnection times and main bonding adequate ) if we have a plastic insert we may omit main bonding on water for example. would supplementary bonding have to be added as it no longer has main bonding ?
  20. Soulcraft Electric

    BISF (British Iron and Steel Federation) prefab houses and main bonding

    Carried out a couple of EICRs on BISF prefabs and on both there is no main bonding to the steel frame of the building. My scheme technical helpline advised that main bonding was not required. Just wondered what people's thoughts are here? These are NOT pictures of the actual lofts (the roof...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock