Search for tools and product advice,
Discuss Replacing ceramic hob for induction - basic questions in the DIY Electrical Advice area at ElectriciansForums.net
Hi all, planning to replace my electric ceramic hob for an induction one.
Current ceramic hob is:
Baumatic B12SS - 230v/400v 3N 50/60Hz 6kW 26.1A, min fuse protection rating 30A.
The current setup is as follows:
CCU>1xB32 MCB>connected to 2x red cooker switches:
  • Switch 1: connected to hob above
  • Switch 2: connected to 2x electric Neff ovens, EACH rated 230/240v 50Hz 3.6kW 16A (models B6774N0GB and B1524N0GB)
Question 1) If the B32 MCB is 32A rated, doesn't that mean that it can support up to a max of 230x32=7.4kW, and if so, 6kW (hob) + 3.6kW (oven 1) + 3.6kW (oven 2), far exceeds the maximum tolerance of this single MCB, when all 3 appliances are at full power? Granted, only on very rare ocassions I have used both ovens plus 4 hobs (Christmas...), and nothing actually tripped. Have I miscalculated the tolerance; is this a safe setup for these appliances?
Question 2) Considering swapping the above hob for 32A wired 7.4kW rated Siemens Induction EX675BEB1E. Is the above setup suitable for a direct swap?
Many thanks
Rupert
you need to take diversity into account.this means that the elements willnot all be drawing juice at the same time, except when initial switch on ( thermostats switching on and off). a 32Acircuit with6.0mm cable has been good for coooking appliances upito 15kW for donkeys, so just connect your new hob. if in doubt, get a local spark to test the circuit.
As above. With diversity, I have your old set up as drawing 38A, and the new one as 40A. As the old set runs ok, can't see the new one not either. If it was a new install, you would probably have two 32A supplies or one 40A.
Many thanks guys. For added info, the CCU is 5 meters apart from both red switches (in case this helps).
CURRENT setup on single 32A MCB: 6+3.6+3.6 = 13.2kW
NEW setup on single 32A MCB: 7.4+3.6+3.6 = 14.6kW
Please forgive my ignorance, checking on NEW setup:
14.6/230 = 63.5A (no diversity applied)
10A + 0.3 x 53.5 = 26.03A (with diversity)
Are my calcs above OK? Is this safe basically because 26.03<32? But what happens when I run all 4 hob zones plus an oven (which is something I do on an almost daily basis)? Will the connection not take it?
Thanks again for your time.
R
Hi - as you’ve calculated, it is possible to overload the circuit with those appliances. The next question - how likely is it? If you were running a restaurant or some such then I’d say it’s not ok and a new circuit is required. If you envisage firing up all 3 appliances together, then for peace of mind I’d run a second circuit if that’s possible.
Interactive User Manual - https://media3.bsh-group.com/Documents/siemens.html?matNumber=9001330662&lang=en
The Induction Hob you are buying has a 'power manager' function which enables the installer or user to set an upper limit on the total power consumed - automatically. So with PM off, the factory setting is for a total inductive heating output of 7.4kW and no more. By selecting PM - look at the link - you can see that the total power can be lowered to suit lower capacity supply (down to a 13A plug). Of course this would mean that when all hobs are in use at the same time on high/full power settings it may take a little longer to first heat up the pans and its contents because a smaller amount of electrical power is spread over the same number of hobs.
Take a look at the reference for further information and setting 'C7'.
So, I would connect up to your current supply and if there are problems you can tweek the maximum power limit. This is what I did for my brother-in-law's new kitchen install and he likes cooking for the 5000 and no-one waits overly long.
Have you actually used yet an IH? They are a MArmite appliance if you get my comparison.
I love my IH... no gas for me, so it's the best option by some distance !
Have not tried it and I'm on the fence about it v gas. Watched lots of vids, articles, I'm aware of the benefits, etc, still, to me going for it v gas will be mainly a matter of managing the risk of gas being banned in future (as they say they might due to climate control), not a matter of preference over the gas cooking experience...
I’ve moved to a property, that’s all electric cooking. We have a ceramic hob, whereas we use to have gas hob. Electric bill has gone up several fold. I read that induction hobs are 50% more efficient, and recent developments make them more user friendly.
I am an avid Speccie reader. In the Feb 19 edition was this interesting article. I am not sending you it to put you off buying an IH, after all they do not all function and perform in the same way and like most good technology over time is perfected. I expect the IH will be 'gas-like' anyway once you are used to it. I have only used the IH a couple of times on cookery courses and was not familiar with the technology and way it heated and so struggled with it. By nature I like simple, tried and tested technology which has been perfected so I tend to be a late-adopter to new stuff such as IHs.
Gas vs inductions hobs: is there any competition? | The Spectator - https://www.spectator.co.uk/2019/02/gas-vs-inductions-hobs-is-there-any-competition/
I've used all types of hob over the years... without a doubt gas is easier, cheaper, more controllable, more versatile and better in most ways. However if you don't have gas... then Induction is the closest... But if I had gas where I live right now.... I'd put a gas hob in within a week ! The only thing I'd miss I think... is the easy wipe clean surface !
Does the entire pan need to be ferromagnetic or just its base? Is it better if the entire pan is ferromagnetic or will it not matter because the sides will never be heated directly by the hob anyway (only the base will)?
Dunno, but I would guess yes, just the base, whatever ferromagnetic is.
I think my old pans (don't have one of those hobs anymore they did my head in!) only had the weird base, not the whole pan was detected. Because if I didn't have the pan just right, it'd pretend to boil my spuds and make me think my tea was nearly ready, but in fact the little blighters were stone cold and rock hard.
So I'm thinking just the pan, or at least on mine. I bet somebody has made better ones now. But it's put me off for life.
Can't beat fire when it comes to man-cooking eh?! :D
Reactions: DPG
Just the base needs to be... but the best pans to used are cast iron ones... they work really well ! I have a few aluminium pans that have had like a ferro-magnetic matrix inserted into the base... they work well too...
Look for this marking: ihpanlogo.jpg
You can test the base of a pan with a magnet to see if it is ferromagnetic. Do not use pure copper, aluminium or tin pans. Using the wrong pan may damage the hob position.
There is actually quite a lot of interesting physics to 'optimise' for a pan to be good for an IH hob; frequency, skin depth, size, base thickness, permeability, hysteresis, eddy currents and their flux patterns, Joule heating, skin resistance........
If you are interested read this link or if busy just the 'cookware' section:
Induction cooking - Wikipedia - https://en.wikipedia.org/wiki/Induction_cooking
Look for this marking: View attachment 52925
Super interesting. Basically paramagnetic metals (Al, Cu) offer less resistance to the induced current thus producing no/less heat whereas Fe based ferromagnetic materials are not great conductors and thus, offer great resistance, thereby heating up! Still, my question was specific about whether a fully magnetic vessel will heat up better than a base-only magnetic vessel. Can't find an answer to that...I guess fully magnetic will be better but not sure the IH plate "cares" about more than the base of the vessel...
my apologies for previous post (since deleted my admin). full of cold, sneezing, eyes dripping like a tap. could hardly see keyboard. thought i had cut it.
Reactions: DPG
Re#20 - fully magnetic pan or just magnetic base pan......
The majority of the magnetic interaction between the hob excitation coil and the pan is taking place in a thin surface layer at the bottom the pan's base. An alternating magnetic field does not penetrate far into a conductor and decreases in depth with increasing frequency of alternation.
The strength of the mutual coupling between the areas/regions on the pan and the hob coils reduces as they become farther apart so again the majority of coupling is to the base since it is flat and adjacent to the coils.
One can also visual that the base will 'shield' to some extent the upright sides of the pan thus reducing further mutual coupling.
Another consideration is that the regions in the sides into which are induced electromotive fields are shorter in dimensions or put crudely small circumference 'circles/bubbles of metal' ; the net electromotive force (emf) around such regions/paths is consequently of low value than in the longer paths/bigger regions of the flat base. Most of the magnetic/electric reaction then to the action of the exciting magnetic field is taking place in the base not the sides.
The large eddy current fluxes caused by the induced emf loops are in the base. And they flow in a thin skin region on the bottom surface. So because it is a thin conducting region the resistance to the electron flows/eddy currents is effectively higher than that of the bulk of the base; beyond the skin depth is in effect 'not used' for eddy current fluxes.
The base is then where the bulk of the interaction takes place between the alternating mag field and currents to flow in the skin layer. In the skin layer these current flows through the skin resistance produces Joule/Ohmic heating of the skin layer (IsquaredR). Thermal conduction of this heat through the pan and thence into its contents results in cooking.
I think the IH makers are working on even higher frequency excitation coils which would allow 'ordinary' copper, aluminium, non ferro stainless steel pans to be used.
The skin depth is approx given by :
What this tells us that the skin is thicker for materials with low permeability like copper and decreases in thickness with frequency. A thicker skin means lower R in IsquaredR so less Joule/Ohmic unless one can increase the size of the eddy currents by more powerful excitation fields.
Copper, Aluminium, non ferro stainless steel happen to be very good conductors and have very low permeability. To employ them usefully for IH cooking pans needs a higher frequency excitation field.
Skin depth in copper
FrequencySkin depth (μm)
50 Hz9220
60 Hz8420
10 kHz652
100 kHz206
1 MHz65.2
10 MHz20.6
100 MHz6.52
1 GHz2.06
Producing high power excitation fields at higher frequencies requires more expensive power electronics than using a lower frequency (20-40kHz) and demanding 'special' pans to be employed.
Briefly, ferromagnetism adds to a pan's goodness for IH because of hysteresis losses manifest as heat.
Or something like this - it gives you the gist of what is going on.
Reply to Replacing ceramic hob for induction - basic questions in the DIY Electrical Advice area at ElectriciansForums.net
Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Hi all, I’m now ready to install my hob, I have a 32A MCB with 6mm T&E feeding a 50A rated switched supply at the worktop. The hob isn’t supplied...
Hi, we are replacing our old hob and cooker and I need a bit of help, to make sure all is safe. This is the oven and hob specs: AEG IKB64401FB...
Hello everyone, Back again after receiving great advice for the bathroom a few months back. This time I'm making a mess in the kitchen. We have...