Shower circuit tripping

Discuss Shower circuit tripping in the UK Electrical Forum area at ElectriciansForums.net

Does it trip if the line conductor is removed from the MCB?

Has the MCB been weakened by someone repeatedly closing it on to a fault (which may no longer be there)?

What was the initial failure? Has the customer had a faulty shower which has been replaced but caused damage to the MCB?

Welcome to the forum by the way.
 
Cable change was probably not required
if the current is constantly below 40A then a faulty breaker is likely, assuming it is just an Mcb.
if it is an rcbo then of course there could be other root causes.
 
Cable change was probably not required
if the current is constantly below 40A then a faulty breaker is likely, assuming it is just an Mcb.
if it is an rcbo then of course there could be other root causes.
Mcb on order only changed cable as easy swap and showed signs on damage and stripped to far back not long enough to re terminate.is there a way to test mcb is faulty?
 

Reply to Shower circuit tripping in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock