You need to check the data sheet.
Some can go direct on to the main live bus as they only need 160A of fusing as last-resort protection so the DNO cut-out is deemed acceptable, others say to put them on a 32A MCB.
You need to check the data sheet.
Some can go direct on to the main live bus as they only need 160A of fusing as last-resort protection so the DNO cut-out is deemed acceptable, others say to put them on a 32A MCB.
thanks for the fast reply?You need to check the data sheet.
Some can go direct on to the main live bus as they only need 160A of fusing as last-resort protection so the DNO cut-out is deemed acceptable, others say to put them on a 32A MCB.
Thanks for the info??Quite a lot are direct on to the bus, less parts and lower series inductance. Usually they are plug-in modules so you can remove them for insulation testing.