Recent content by bigspark17

  1. bigspark17

    Rcd main switch on tncs system

    As title, what regulation does this not comply with? Thanks
  2. bigspark17

    Tennis court lighting

    If it were me id ask how many lumems they require on the playing surface, map out the poles on a diagram with size of playing surface and pole heights then take this information to a lighting specialist and they will do these calculations for you and give you a spec.
  3. bigspark17

    Oven and hob diversity

    this is when diversity calcs are pointless. If the whole oven and hob is on then you need to accomadate for that because it is possible, most of the time they wont and all ovens and rings have stats so they are not going to be, but this diversity calc is as much of a joke as the maximum demand...
  4. bigspark17

    32 Amp Cooker Circuit 13 Amp Cooker

    Ive started fitting these now, i dont love the 13amp fuse behind the appliance but rarely blow unless there is an issue and only 2 screws to access. Could mount in cupboard adjacent but no good if its drawers
  5. IMG_9773.jpeg

    IMG_9773.jpeg

  6. bigspark17

    Using old 2.5mm t&e with 1mm cpc

    Yes as far as i see it your not making the circuit any worse, if zs values are correct then i struggle to justify not altering the ring final, especially as the consumer unit is otherside of property and floor is byson beams 🙈
  7. bigspark17

    Using old 2.5mm t&e with 1mm cpc

    Thanks for response. Can you suggest the calculation i would need to satisfy this? Many thanks
  8. bigspark17

    Using old 2.5mm t&e with 1mm cpc

    Can i add additional sockets off a cirvuit that uses 1mm cpc within a 2.5t&e cable please? Or can i use it to feed a switch spur then 2 x sockets?
  9. bigspark17

    110v consumer unit

    Thanks for the reply. Is this for isolation? The main switch is 2 pole. What section of the regs guides this? Thanks
  10. bigspark17

    110v consumer unit

    Hi, not experienced this before but i have a workshop where the 110v consumer unit (old wylex 3036 board 4way) Do the board is fed from a 16amp sp mcb from a t0&n board. Then goes into. Standalone transformer wall mounted 3.5kva then into the cu and then to 4x 110v socket outlet. Ive managed...
  11. bigspark17

    What is this earthing arrangement?

    TN-S i would say. What was your ZE? I wouldnt take the old cert info as gospel. You have no idea who tested that or if they actually did?
  12. bigspark17

    Are Quinetic still regarded as the best kinetic switches?

    Hi. It does Make me wonder if you were doing al this work why would you not use traditional switching? Do they need to be able to dim there kitchen lights on the app while sitting in the kitchen? Strange application. I hope that adaptable box was easily accessible
  13. bigspark17

    Earthing roof beams and roofing sheets on an attached garage.

    Not really its clear in black and white. Not knowing the regs isnt the regs books fault.
  14. bigspark17

    3 phase surge on reenergising panel board

    Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin gerin panel board) over the next 30 mins customers on park are reporting loud bangs inside some of there vans, boilers and electric fireplaces (with...
  15. bigspark17

    Do air-to-heat systems work with smart thermostats and radiator valves?

    Sounds like you have an air source heat pump. Yes it usually can be controlled by external controls. A job for your local electrician :)