  1. westward10

    What do these ratings mean

    I didn't see the 13A. 10A for 230v is cutting it fine and 10A for 240v is too low.
  2. westward10

    What do these ratings mean

    In simplistic terms the resistance is constant but power (kw) will change proportionately with the applied voltage. So for 230v the power is 2.3kw and for 240v it is 2.5kw. The 10A fuse satisfies 230v and the 16A fuse satisfies 240v, I suspect 13A fuses which would satisfy both is not included...
  3. westward10

    3A fuse instead of 13A?

    The 3A fuse is there to protect the current lighting. For additional power you connect from the non protected 3A fuse side.
  4. westward10

    Emergancy work flow

    I was going to suggest the brewery chains but you are likely to need nationwide coverage and the chances of a small enterprise getting a contract is all but zero. Commercial refrigeration is another as down time can be very costly.
  5. westward10

    Single Phase Puzzle to challenge you

    It has brushes?!
  6. westward10

    New Bathroom Extractor Fan - Wiring Query

    The yellow is the trigger wire to activate the fan.
  7. westward10

    New Bathroom Extractor Fan - Wiring Query

    The yellow is not earth I would strongly recommend you get an electrician to do this.
  8. westward10

    external socket on ring or radial

    Why aren't you asking them?
  9. westward10

    external socket on ring or radial

    Who will be notifying building control?
  10. westward10

    EICR - Help on my Request for Electrical Safety Alternatives and Quotes

    As I said it is questionable and my query was perfectly correct. For you to suggest a 2.5 on a 25A protective device is fine without knowing the installation method is, well, questionable. Not sure how the 32A protective device being type B is relevant.
  11. westward10

    3 phase dB and eddy currents

    Three phase or single phase it is not correct.
  12. westward10

    RCBO installtion in old MCU following EICR Report

    They stick out no more than the already fitted RCD.
  13. westward10

    RCBO installtion in old MCU following EICR Report

    No contact them with a picture or part number if you have it.
  14. westward10

    UK Earth bonding to Water

    No.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock