Hello all, I hope you're all keeping well.

I have a question regarding insulation resistance testing.

Whether doing a single circuit IR test or a global IR on an entire installation, I usually try to remove all loads, eg lamps, neons etc, but obviously this isn't always possible. So I generally join both L+N and test to earth. This is to avoid damaging any sensitive equipment by ensuring no potential difference across the load.

But how come I still can get a bad reading on a circuit while testing this way? I don't fully understand. Is it due to certain loads being able to throw up a bad IR reading and others not?

Any help would be greatly appreciated
 
If this is a global reading you need to break it down to individual circuits by disconnecting the neutral conductors and having all protective devices off. What test voltage are you using.
Having something still connected should not matter unless that something itself is faulty.
 
Some older RCD sockets/spurs will give a low IR to E, without apparently being defective. Surge protection (eg extension leads) will give a low IR when tested at 500V (but not at 250), typically about 0.4M ohms. Anything with a functional earth will again give a low IR to E, in my experience this is only likely to be certain RCDs or RCBOs at a downstream CU.
 
Having something still connected should not matter unless that something itself is faulty.
The use of MOVs between L and PE and N and PE is not that uncommon this will cause low IR measurements and not be faulty.
 
Metal oxide varistors, also known as MOVs are one of the most common types of varistors designed to protect electronic devices and electrical circuits against voltage surges and spikes by changing their resistance.

[ElectriciansForums.net] Insulation resistance testing live conductors to earth
What is an MOV?
 
There can be a few reasons for low L+N -> E readings:
  • Connected equipment is leaking. By design, or just old/damp
  • SPD are connected (but there you get a big difference between 250V where usually > 10M and 500V where usually < 0.1M)
  • Cable has degraded or is very damp
  • Accessories are damp/dusty
If a global IR is good, as in above a few M, then you know all circuits are similar.

If the global IR gives you cause for concern, say as it is < 1M, then checking individual circuits can at least establish if a low total is due to, say, 10 decent circuits of ~5M leading to ~0.5M, or 9 are > 10M and one is deeply suspect as different at ~0.5M, etc.
 

Reply to Insulation resistance testing live conductors to earth in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
250
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
273

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top