Discuss Relay Design and Wiring in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current sensor and a delay off timer relay. It is the sort of thing one might use with work shop power tools for automatic switch on and delayed off for a chip extractor with a manual override to run the extractor independently of the power tools operation.

In essence the chip extractor will run when a power tool is switched on, The dust extractor will run until the power tool is switch off but with say a 10 second delay (dust extractor runs on for 10 seconds after power tool switched off). There should be an override button to allow the chip extractor to be run independently of the power tools together with an off button to stop the override. Indicator lights to show whether the system is in Auto (delayed Time off mode) - Blue light, Override Mode - Green light or Off Mode - Red Light.

The normal state of the system should be off and showing a steady red light. When a power tool is being used the system should show a Blue light (Auto mode) whilst the delayed stop timer relay is activated and a Green light when the system is operating in override mode.

The components are:

  • a Green Brook PRR208 -230 VAC DPDT (changeover) 8 pin 10 amp relay with 2 NO and 2 NC switch terminals and base,
  • a delay off adjustable timer relay 250 VAC 16amp 50/60 Hz and,
  • a self powered current sensor switch adjustable 0.3 ~ 30 amps normally open
  • a momentary RED push button switch with both N/O and N/C contact terminal choice
  • a momentary GREEN push button switch with both N/O and N/C contact terminal choice
  • LED indicator lamps 230-380V 20mA in Red, Blue and GREEN
  • 1 x Single gang 13A power socket outlet wired to the main relay - for dust extractor power
  • 3 x double gang 13A power socket outlets wired in parallel - for power tool power
  • Power source - single phase 240VAC on a 32A rated breaker
  • Dust extractor - 1,200 W 230V - max current draw 5.22A

The dust extractor is powered from a single 13 amp socket outlet running through the change over relay rated at 10amps. The power tools are powered from 3 x 2 gang 13amp socket outlets.

I think my logic of how the circuitry works is generally correct, however the one problem I am having is to understand how I can wire the system so that the override light is off when socket outlet no. 4 is being powered when the timer relay has been triggered and is controlling the power to the socket outlet. Perhaps I need an 11 PIN relay. I tried designing it with a DPST NO relay but this didn't give me the flexibility I needed.

The light indicator logic should be:
  • Auto mode - power tool use (current flow) determines power to dust extractor - Blue light on, RED light off, green light off
  • Override mode - Green push button operation latches CR1 relay coil - GREEN light on, Red light off, blue light off
  • Stop mode - Red push button cuts power to override circuit putting CR1 relay back to unenergized state - STOP light on, Blue light off, Green light off
If anyone is able to help with the logic and to solve my indicator light issue I would much appreciate the help and any suggestions/comments as to how to resolve the issue.

I would also appreciate to know if my ladder diagram wire numbering is correct. I am not sure I fully understand how wire numbering is applied.
 

Attachments

  • Forum Schematic Circuit Diagram.pdf
    130.1 KB · Views: 27
  • Forum Schematic Ladder Diagram.pdf
    101.3 KB · Views: 24

By the time you have wired and re wired the relays to suit your needs, you would find you are better off with something like this.

Dead easy to program, drag and drop ladder logic.
Probably not much more than your relays.
You will still need your current sensor though.
Thanks James but seems like a much more expensive solution to me. This for me is more about learning how to wire relays from scratch and the logic.
 
You can get rid of most of the complication with a simple 3 position switch for Auto-Off-Manual.

Your ladder diagram doesn't work, I think the biggest issue is that you are trying to represent physical relays and wiring on a ladder diagram when it is a programming language which provides the instructions to a PLC or programmable relay.

If you want to play around with ladder logic you can download the trial version of the Siemens logo software which allows you to draw ladder diagrams and simulate them, you just can't download a program to a logo from the trial version.
 
You can get rid of most of the complication with a simple 3 position switch for Auto-Off-Manual.

Your ladder diagram doesn't work, I think the biggest issue is that you are trying to represent physical relays and wiring on a ladder diagram when it is a programming language which provides the instructions to a PLC or programmable relay.

If you want to play around with ladder logic you can download the trial version of the Siemens logo software which allows you to draw ladder diagrams and simulate them, you just can't download a program to a logo from the trial version.
Dave thanks for this. I appreciate what you are saying regards the 3 way switch and already considered this but I wanted to try and work it out using lights, push buttons and relays more as as an intellectual exercise and for learning purposes.

As for the ladder diagram I was following this guy amongst others on:


So I suppose there are more than one way of doing ladder diagrams and what they are used for. They are also used for air conditioning systems I understand.

Thanks anyway for your time.
 
So I suppose there are more than one way of doing ladder diagrams and what they are used for. They are also used for air conditioning systems I understand.

I watch a YouTube channel that repairs pinball machines and the old pinball machines use ladder diagrams for the relay logic.
 
Thanks I'll take a look and see if I can find it.
Maybe not the channel Spoon was thinking of but one called Technology Connections has done some features on old pinball machines.

Ladder logic can absolutely represent physical relays, that's where it started. In regards to your system, I wouldn't switch the extractor through the 8-pin relay, their contacts are not up to the job despite saying 10 Amp. Rather I would use the relay to switch a stronger contactor that powers the extractor.

Keep working on your diagram, as Dave said there are some issues that will stop it working as you intend so come up with a V2 and we'll take another look.
 
The guys who I watch every now and then are these
 

Reply to Relay Design and Wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
744
Hi Everyone, New to the forum but hoping I can find a little help with my restoration project... I am adding a secondary wiring "system" to my...
Replies
14
Views
988
Good Morning need some advice please. Yesterday went to change a light fitting in hallway. There are two ceiling lights in the hall controlled by...
Replies
6
Views
246
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
585

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock