The equiptment hasnt been installed as of yet so no info. So you are saying i can come off the incoming side with fused protection to the em stops to control the contactor?
Because when you kill the board via the main switch there is still a live circuit.somebody working on the circuit at a later date may not realise this.
It was more along the lines of regarding the em circuit you cant come off the load side and you cant come off the mains side as it would be bad practice even with an inline fuse etc.
Hi. Im looking for the best advice for wiring an emergency stop circuit controlling a dis board via a contactor. This is a dis board feeding circuits in a workshop so the whole dis board must be de energised when the stop button is hit. The problem being the contactor is fed from the dis board...