Recent content by Grandplan

  1. G

    2KW oven and 6KW hob on B32 MCB

    Yes you can - but - I think you will need to connect both supplies to FCU's below the outlet. Otherwise you'll have a 1.5mm2 cable (max current carrying capacity 16 A) and a 2.5mm2 cable (max current carrying capacity 25A) only protected by a 32A MCB
  2. G

    Extract Fan 1 Amp fuse - but UK only

    Hi All, Been asked to fit a bathroom extract fan that a customer has already purchased. When checking the manufacturers instructions they are stipulating a double/ triple isolating switch - nothing unusual there - but they are then stipulating a 1 Amp fuse and then in brackets 'UK Only'. This...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Advert

Back
Top