Yes you can - but - I think you will need to connect both supplies to FCU's below the outlet. Otherwise you'll have a 1.5mm2 cable (max current carrying capacity 16 A) and a 2.5mm2 cable (max current carrying capacity 25A) only protected by a 32A MCB
Hi All, Been asked to fit a bathroom extract fan that a customer has already purchased. When checking the manufacturers instructions they are stipulating a double/ triple isolating switch - nothing unusual there - but they are then stipulating a 1 Amp fuse and then in brackets 'UK Only'.