Recent content by Tooly1

  1. Tooly1

    16mm twin and earth main supply?

    Again, you've put that across very well, many installations out there still that are in good working order, maybe more than the latter ones, unfortunately.
  2. Tooly1

    16mm twin and earth main supply?

    Yeah this is what I have it as Thanks for the clarity. In essence, it's worth noting and just making them aware. I suppose with these EICRs, a lot of installations are still in good working order; it's just our ever-changing landscape of the IET regs that keeps us on our toes!
  3. Tooly1

    16mm twin and earth main supply?

    No it's ran in the stud wall.
  4. Tooly1

    16mm twin and earth main supply?

    Sorry the landlord / building operator believes it isn't an issue and has never been flagged previously. In the previous job notes it stated a electrical danger notice was issued for bno equipment also but not highlighted the danger.
  5. Tooly1

    16mm twin and earth main supply?

    16mm twin and earth main supply to storage heater board, no mechanical protection or earthed outer sheating ? No upfront rcd only a bs1361 50amp fuse. Here’s the updated version including your Observation: The inspected apartment contains two consumer units. We were instructed to carry out an...