Rockingit

~
Mentor
Arms
Hello all, been a minute....

Totally selfish question as this is all about me, or rather my inconsistent energy (and no, not talking about middle aged blue pills....)

The place I occasionally get to spend time in and call home is very rural, middle of Somerset, less a village and more a hamlet. We're increasingly suffering from 1-5s sort of duration power cuts, at least one a week and often more, none of which ever get a mention on the outages listings on Western Power. Now, to my mind these can't be deemed as 'faults' simply as they're always way too short, it's more like a changeover event upstream, but that would count as 'planned' and ESQCR has a lot to say about that in terms of notification to users. In days gone by I could just ring up the regional depot at Exeter and speak to the duty engineer and have a professional conversation but of course that's now long gone. I'm aware of all the issues (that we all predicted....) to do with the Grid not being up for the job now we've got EV's and Solar, over-voltage and so on but that doesn't really 'fit' around here, we have overhead lines at about 242v that suffer drop around milking time when the dairy parlours all fire up!

So before I start some Victor Meldrew style assault on a call centre that's never heard of ESQCR let alone been 'trained' to deal with people who actually understand their product better than they do, is this now just becoming a National 'thing' and I'm behind the news.? It's seriously starting to feel like living in the third world.....

Welcome people's thoughts......

R.
 
11kV overhead networks typically have delayed auto-reclose circuit breakers at the primary substation and often other pole mounted devices which carry out similar duties. The vast majority of faults on overhead 11kV networks are transient - lightning induced flashovers, wind blown debris that drops off/blown away, tree branches contacting the bare OHL conductors etc - so automatically re-energising the circuit is usually successful without a control centre involvement. Source breakers typically have a reclose time of 10 seconds, though some pole mounted devices can have a much shorter reclose time. It's many years since I was involved with 11kV networks, so whilst the principles remain the same, there are probably more sophisticated pole mounted devices around these days. Faults which result in successful auto-reclosure wouldn't be listed as outages by the DNO. If it persists, it would be worth taking it up with the DNO as there may be overhead line defects of which they are unaware, if the pole mounted devices (not remotely monitored) are operating frequently.
 
The power around my way in the Midlands is not too bad. Probably just jinxed it mind.

But had issues with internet no end. But that's for another thread.

Must be really annoying when it loses some power and you know it's cows being milked. That industry needs all its tax breaks cutting off so we can see where it is really. It has been supported by the nation and governments for so long nobody knows the real value anybody is "losing" to eu or abroad or whatever anymore.

Should be treated like an average business, like poundland should be also. It didn't make profit a long time ago so was already broken before liquidators purchased it. The dairy should be sold at profit or not at all if they don't profit. Nobody should be helping keep farms running when they don't make money.

The milk isn't the issue it's the business model. IMO anyway.

Are they not lapping up the sun down there using Solar? and wind near the coast with windfarms?

Seems old skool to be connected to the grid if they need so much power suddenly.
 