Working in school kitchen,they have a hot warmer & lights to keep food warm
Pulled out plugs ,really hot & on pins too.
Checked socket connections ,they were ok,face of socket warm.
They are mouldered plugs,no sign of over heating,but ridiculously warm.
The equipment is 2.8 kw.
 
Working in school kitchen,they have a hot warmer & lights to keep food warm
Pulled out plugs ,really hot & on pins too.
Checked socket connections ,they were ok,face of socket warm.
They are mouldered plugs,no sign of over heating,but ridiculously warm.
The equipment is 2.8 kw.
This is common when you get near to 3kw.Cheap plug tops tend to get warmer than branded products.
Regards,S
 
Socket contacts may be weak or dirty, also fuse clips in plug. There's no reason why a plug should get 'hot' at 2.8kW, although they tend to get warm.
 
Are the plugs constantly being plugged and unplugged on a daily basis? As above swap the plug tops and socket outlets.

Is it feasible to swap for SFCU?
 
Are the plugs constantly being plugged and unplugged on a daily basis? As above swap the plug tops and socket outlets.

Is it feasible to swap for SFCU?
They are switched on in morning bout 8 & off bout 3.00pm.
Not too much attention when pulling plugs out of sockets but with this,you know as soon as you pulled them out.
 
Working in school kitchen,they have a hot warmer & lights to keep food warm
Pulled out plugs ,really hot & on pins too.
Checked socket connections ,they were ok,face of socket warm.
They are mouldered plugs,no sign of over heating,but ridiculously warm.
The equipment is 2.8 kw.
Could be a loose wire in the plug or socket.
 
Perhaps the appliance is faulty and drawing more current than designed

Unlikely, with a normal heating appliance. Plus, if it is drawing too much current it will be getting too hot, and that is more likely to be noticed than the plug.

This is simple. The weak link in any plug and socket is the tiny contact area between the two, where the socket grips the pins. Even the most expensive, high tech connectors are not perfect, and the humble 13A socket certainly isn't in its cheaper forms. If the contacts get slack or the pins are tarnished they will heat.

A good quality 13A socket/ plug combination will handle 13A semi-continuously. We should not have to suggest that a 2.8kW load is excessive so that the appliance has to be fitted to an FCU. A 16A socket would be better but should not be necessary. Maybe these sockets have been abused, maybe worn or grimy inside, or just a poor design from new. But changing them, and the plugs if needed, should solve the problem.
 
I have been into many site offices where they have had a heater on the wall plugged in via 13A plug and the socket has brown heat marks around the pins where there is a long period of an on/off cycle. A switched fused spur is more suited. What is the F.L.C. if a plug and/or a flex has been put it could be the F.L.C. is more than 13A and should have been hardwired or via 16A socked radial circuit.
 
If the pins and/or socket connection has become tarnished over time there will be a higher resistance between the two, which could well cause overheating.

Unplugging it and plugging it in on a regular basis will help keep the contacts clean. Maybe try it a few times while you're there.

A more substantial solution may be, as suggested, to wire via FCU if it's not going to be moved, or commando plug and socket if it is.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
What you reckon,very warm/hot pins
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
26
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
cliffed,
Last reply from
littlespark,
Replies
26
Views
3,354

Advert

Back
Top