are you suggesting I leave the current arrangement but connect it to a spike via 16mm cable to the henly block?
If so, what do I put on the cert?
I think I may have sussed this out
I managed to follow the poles back to th trannie; Two wires,,, and then to the pole where the supply splits between the house and the lodge three wires but the third not connected ????
on to the house,,,scrambled down a banking (next to 50ft waterfall) to get a butchers at the connection
EUREKA!!! SWA into the house is fed from the three wires L,,,N,,, E but E & N connected together at the top of a pole that cannot be seen from anywhere without descending into the ravine.TNS methinks
Question is; why does the earth cable go go back into the wilderness for 200yards and not teminate into anything when it is connected to th Neutral 10 FT from the house?