hi looked at a job today 32a mcb feeding outbuiding CU. out building cu has 20a mcb for radial sockets is this ok re discrimination (mcb's in series) im sure it is but thought there was a specific ratio
 
The MCB's will discriminate on overload, but not on short circuit. If you want to achieve complete discrimination, then change the 32A Mcb for a 32a fuse. You can buy fuse carriers that are direct replacements for MCB's
 
is that a requirement under bs7671 complete discrimination? 536.1 refers to fault currents
 
Last edited by a moderator:
I think it comes down to convenience to be honest. In a domestic situation, it's not really going to matter much if you lose the upstream breaker because someone puts a spade through a cable. In a commercial or industrial setting this could cost a lot of money.
 
thats my thinking too not a huge problem in domestic ,under fault conditions (short circuit) its virtually impossible for cascading mcbs to provide assured discrimination. but a 30amcb to a 20amcb should provide some form of limited discrimination in the event of overload.
 
in any event a short circuit or fault condition would trip the rcd protecting the sub main any way long before either of the mcbs even tried to open so actually electrically it appears a mute point. wanted to be clear on the reg though
 
Last edited by a moderator:
why ?? a fault on the 20amp socket radial would trip the rcd protected sub main, or it should. just pointing out that discrimination between the 30a mcb and 20a mcb is irrelevent under these conditions as the power will be disconnected via the rcd
 
Last edited by a moderator:
why ?? a fault on the 20amp socket radial would trip the rcd protected sub main, or it should. just pointing out that discrimination between the 30a mcb and 20a mcb is irrelevent under these conditions as the power will be disconnected via the rcd
Is an RCD not there to provide additional protection against earth fault and not short circuit?
 
I thought the rule of thumb for MCB discrimination was twice the value IE a 16 Amp MCB will discriminate with a 32 Amp MCB.

I read it in one of the 17th edition guides somewhere, if the upstream device is less than twice the value of the downstream device then discrimination will not occur, or put another way if the upstream device is twice the value of the downstream device then discrimination will occur.
 
yes sorry i meant short to earth when i said short circuit sorry was very unclear pls accept my apologies. for a direct short circuit between line and nuetral the mcb's would open but i doubt if discrimination would be possible due to the high fault.
 
yes i have seen somthing similar but i thought that was for fuses not mcb's ?? i dont think discrimination in cascading mcbs is possible when it comes to fault conditions
 
Last edited by a moderator:
anyway does a 30a mcb feeding a 20amp socket radial contravene any regs re discrimination as that what the customer currently has.
 