ianphilip007
hi looked at a job today 32a mcb feeding outbuiding CU. out building cu has 20a mcb for radial sockets is this ok re discrimination (mcb's in series) im sure it is but thought there was a specific ratio
in any event a short circuit or fault condition would trip the rcd protecting the sub main any way long before either of the mcbs even tried to open so actually electrically it appears a mute point. wanted to be clear on the reg though
Is an RCD not there to provide additional protection against earth fault and not short circuit?why ?? a fault on the 20amp socket radial would trip the rcd protected sub main, or it should. just pointing out that discrimination between the 30a mcb and 20a mcb is irrelevent under these conditions as the power will be disconnected via the rcd