any body wired up a sunbed shop before!!

what method of installation did you go for and what cables did you put in...!!

the shop in question will have 3 beds (3 phase stuff) looking at 6mm supply on a 32A TP MCB, not sure if i should install in tray over head (above tiles) or in singles in my dado system along side my sockets and coming off to my individual beds in nice flexy copex (63a rotarys will be insalled in DB room approx 1 meter away from all beds)


HELP...!! lol
 
if you use the dado, then you may find that you have to derate the cables a little, because im guessing that its either full load or nothing, so little diversity to be applied if any.
I would consider using either SWA or rubber flex on tray (whichever is cheaper).
 
i have increased the CSA from 4mm (20A) to 6mm (32A) to allow flexibility... im still awaiting the final paperwork from manufactures as per the spec and KW rating... either way nice inductive load on a type C...

i have though about rubber flex on tray... that will be last resort above ceiling if i have too..! :)
 
i've done 3 phase sunbed installs at a gym :-)

used 5 core 2.5 flex installed in a mixture of surface mount pvc conduit and trunking with main cable runs under the floor / drilled joists etc , giving 20A per phase at each unit , which is more than enough ( 32a seems a bit overkill )
Connect the cable to rotary isolators near to where the beds are to be located and the bed installers will usually connect up
 
Think you had better wait for that spec to the sunbeds, as some of these units are real power hungry monsters... lol!!
 
12.5 - 15kw per bed... 3 phase 4mm supply should do the trick. That will drop 25 amps per phase easy and also combat the massive volt drop of 15 meters!! Not to mention de rating factors of been squashed tightly in compartmented dado trunking Alongside air. :)

All wiring is surface mounted through out the building!! Sounds too easy!!

Oh yes one obstacle!! The building currently obtains power single phase from an unknown metered supply!! Looks like more paper work for me with NEDL.
 
Last question !! I'm probably going to fit a large wall fan Ifi can get it in any suggestions???
 
Last question !! I'm probably going to fit a large wall fan Ifi can get it in any suggestions???

I fit a lot of greenwood 9 inch with rc4 controllers and they're pretty reliable. You could look at fitting 2 so 1 could be set to input and 1 extract to keep changing the air.
 