I have just connected up a shower for a customer on a RCD unit seperate from thier main board which has no RCD protection

They have a TNS system and I got a Ze reading of 37.5ohms Am I right to presume the shower is safe as it is on a RCD but the rest of the house isnt? And cant work out why the reading is so high?

Grateful for any help....
 
if the Ze is that high, then a call to DNO to rectify is your next move. it's their problem, let them sort it.
 
would def get dno out.

wouldn class it as unsafe as TT's can be higher than that . however since its a TNS id check all other circuits to make sure they are on an rcd , if not they wont meet disconection times

EDIT : didnt read post correctly, No rcd as you stated . get the DNO asap . ( possible a dangerous situation report to customer )

- - - Updated - - -

With figures like that it sounds more like a TT!


Let us know what the DNO say!

my thoughts too
 
I hope you havnt left it that way ???? from what you say the rest of the house is not on an RCD therefore would be potentially a fire/shock risk. Get DNO out, it is classed as an emergency and they will respond within 3 hours.
 
I have had no choice but to leave it that way I have told the customer and offered to put in an rcd or new board and adviced them to call the DNO first I have noted it on the test certificate to cover myself .Will have to see what happens.
 