Customer moved bathroom few years back, i turn up and dno fuse is under the sink!!! CU is in cupboard under stairs. Someone must've extended consumer tails. So... C1 or C2? I think C2 as that means if something (water!) happened it would be dangerous. C1,c2 are brilliantly vague. Looking at esc guidance still got no idea.

Ta

Ed
 
Extended tails I would most likely not give it a code, as there is nothing in the BGB regarding tail length and so therefore what does it fail on with regards to the BS 7671-2008. I may inform the customer that if they are over 5 metres say there is a recommendation that the tails be protected, but I think that one would be ignored, unless you have a very understanding customer

As for the DNO fuse under the sink, again no code as it's bugger all to do with us. Again I would advise the customer of the dangers of this and what theoretically can happen.
 
I wouldn't want it in my bathroom, what happens when I'm really drunk and wee in the sink, and around the sink!!! (I don't really do that!)

Hmm its not a switch or socket outlet, but it must be within the zone around the sink, so its unsuitable for its location. C1 or C2 and it fails anyway.

The dice say C2...
 
I agree with Malcolm it does not fall into the remit of BS7671 but both issues need to be covered in additional information and on a covering letter. If they were coded they would not be C1 because a fault has to occur for there to be a problem so they are not immediately dangerous.
 
I agree with Richard agreeing with Malcolm
icon14.png
icon7.png
 
You could always check with local DNO who will provide the info for the maximum tail length they allow which is in the OSG but due to regional variations it cant be noted with a compliance or non-compliance
 
Taken from EAWR89

Regulation 7 Insulation, protection and placing of conductors
All conductors in a system which may give rise to danger shall either -
(a) be suitably covered with insulating material and as necessary protected so as to prevent, so far as is reasonably practicable, danger; or
(b) have such precautions taken in respect of them (including, where appropriate, their being suitably placed) as will prevent, so far as is reasonably practicable, danger.
109 The regulation requires that danger be prevented, so far as is reasonably practicable, by the means detailed in either part (a) or (b).
 
I would say C2 for the cutout - the customer moved the bathroom after the cutout was installed! The Cutout is not upto IPX4 (I bet) so it should not be within zones! - C2 all day long

As far as tails - C2 again unless they are heat shrinked and waterproof - if not IPX4 then C2.

Just remember with coding:
C1 = Immediate risk to life!
C2 = Risk to life if a fault occurs
C3 = Recommendations

Coding is easy - just think if someone can touch that and be killed then C1, if someone can touch it but only get killed if a fault happens at the same time then C2, not upto regs then C3.

A fault is anything is not meant to happen which includes pooring water over a DNO cutout
 
I thought EAWR only applies at work thogh?
I agree with malcolmn, I would give it an observation on my test sheet, maybe quoting 'EAWR adequacy of access to equipment' However since your comparing the installation to bs7671 im not sure I could code it any higher then that!
 
Nicholas - you could apply the same logic as yours to any electrical point/wiring below pipe joints
i.e. The kitchen thats below the bathroom - would you give that pendant a C2 as if a pipe burst it could fill it up?

Malcolm hit the nail on the head.
 
The EAWR99 applies everywhere where electricity is used.

Everyone has a duty of care over themselves and everyone who is in the area (including a home if a visitor comes in)
 
Nicholas - you could apply the same logic as yours to any electrical point/wiring below pipe joints
i.e. The kitchen thats below the bathroom - would you give that pendant a C2 as if a pipe burst it could fill it up?

Malcolm hit the nail on the head.


I see your point but the kitchen is not a zone of the bathroom. Its a different room.
 