david911cockbur

Hi All,

I recently heard about the sad death of Emma Shaw who was electrocuted mopping up a water leak in her airing cupboard, apparently a plasterboard screw had caught a cable and caused the metal stud partitioning to become hazardous live!
Strangely the problem was then blamed on a lack of insulation resistance testing even though an insulation resistance test will only measure the resistance of insulation between circuit conductors; and circuit conductors and earthed conductors???
The partitioning upstand could not have been earthed or the over-current protection device would have automatically disconnected the circuit the first time it was switched on!

Any thoughts?
 
a fully functioning RCD should have tripped before the current reached a level that was fatal.
 
Hi All,

I recently heard about the sad death of Emma Shaw who was electrocuted mopping up a water leak in her airing cupboard, apparently a plasterboard screw had caught a cable and caused the metal stud partitioning to become hazardous live!
Strangely the problem was then blamed on a lack of insulation resistance testing even though an insulation resistance test will only measure the resistance of insulation between circuit conductors; and circuit conductors and earthed conductors???
The partitioning upstand could not have been earthed or the over-current protection device would have automatically disconnected the circuit the first time it was switched on!

Any thoughts?

First thought - not at all sure how you can arrive at conclusions unless more information is available. There needs to be certain conditions present for the above to be possible at all - was an RCD fitted to the board? We know nothing about the install to be able to draw those conclusions.....
 
telectrix,
Hello again, are you going to explain how an RCD would have saved the day, or are you just on the wind up again?
 
if it was studwork and was live,and wasn,t earthed no test would have picked up a fault
i think tel is saying the rcd should have tripped before she received a lethal poke
its all conjecture though
tin hat at the ready
 
that's exactly what i meant. the whole point of RCDs is to trip out before the current passing to earth through a body reaches a fatal threshold. determined by better minds than mine at 30mA.
 
hi tel, ive just been reading the info on google i cant post the link as its pdf
it seems there was no rcd she had contact with the water on the floor it had gone under the studwork that was live and tryed to turn off the stop cock and died
the test certs were botched by an unqualified mate too
google "unlawful killing iet electrical"
 
Last edited by a moderator:
First of all f&r we're talking about a dead girl here so cut the sarcasm!

telectrix - 2mA is the lethal threshold, who told you it was 30mA?
 
Hi ayjay,
If the affected circuit was a lighting circuit the RCD becomes irrelevant.
If the conductive stud work had been earthed, the fault would have had to be found before hand over as the circuit wouldn't have stayed on.
 


2mA is the lethal threshold, who told you it was 30mA?





That may or may not be the case
If it was used as the figure to protect electrical installations they would become un usable
Trying to protect against that level would not be practical

We are where we are, with 30 m/amp decided upon high being the sensible protection
 
Last edited:
Thanks Des,
It is well documented that 2mA can be lethal if the duration is long enough; and you're right 30mA is just a limit that has been chosen for the sake of practicality and limiting nuisance tripping. So where did this rubbish come from about 30mA trips preventing deaths indoors?
 
telectrix - Are you actually an electrician?

2mA at a supply voltage of 230v is lethal if the duration of the shock is long enough!
 