Octopus
So a few weeks back I was asked to install an extra socket close to the CU - on the face of it an easy job, newish board, spare capacity, easy run under the floorboards - so I sent an estimate and went to do the job a couple of weeks later.
On the day, I took the cover off the board and did a Ze to discover that the house didn't have an earth at all. Called UKPN and then came out late last week (about 4 weeks after my call) and converted it to PME. So I got a call from the owner to say come back...
So today I went, 16mm GY in hand and ran the cable the 1m or so to the board.....
As soon as I connected the GY to the board one of the RCD's tripped. Hum I thought.....
(I should add that in the intervening period the customer had got the EIC from the previous sparky - who had a reading of 0.28 for the Ze and all good IR readings for the circuits, plausible readings for R1 + R2 etc and the RCD trip times....)
So in failing light, I noted that using an upstairs socket would trip the opposite RCD, and activating the cooker circuit would also trip the same opposite RCD.
All the cables in the CU are a mess, a combination of red/black and brown/blue with choc block and joints and changes of colour....
So my Saturday is now going back to "unpick" all the circuits and reconnect them.
What a shambles and to think so twxt of a sparky has left this in such a state makes me dispair!
Rant over.....
On the day, I took the cover off the board and did a Ze to discover that the house didn't have an earth at all. Called UKPN and then came out late last week (about 4 weeks after my call) and converted it to PME. So I got a call from the owner to say come back...
So today I went, 16mm GY in hand and ran the cable the 1m or so to the board.....
As soon as I connected the GY to the board one of the RCD's tripped. Hum I thought.....
(I should add that in the intervening period the customer had got the EIC from the previous sparky - who had a reading of 0.28 for the Ze and all good IR readings for the circuits, plausible readings for R1 + R2 etc and the RCD trip times....)
So in failing light, I noted that using an upstairs socket would trip the opposite RCD, and activating the cooker circuit would also trip the same opposite RCD.
All the cables in the CU are a mess, a combination of red/black and brown/blue with choc block and joints and changes of colour....
So my Saturday is now going back to "unpick" all the circuits and reconnect them.
What a shambles and to think so twxt of a sparky has left this in such a state makes me dispair!
Rant over.....