Octopus

So a few weeks back I was asked to install an extra socket close to the CU - on the face of it an easy job, newish board, spare capacity, easy run under the floorboards - so I sent an estimate and went to do the job a couple of weeks later.

On the day, I took the cover off the board and did a Ze to discover that the house didn't have an earth at all. Called UKPN and then came out late last week (about 4 weeks after my call) and converted it to PME. So I got a call from the owner to say come back...

So today I went, 16mm GY in hand and ran the cable the 1m or so to the board.....

As soon as I connected the GY to the board one of the RCD's tripped. Hum I thought.....

(I should add that in the intervening period the customer had got the EIC from the previous sparky - who had a reading of 0.28 for the Ze and all good IR readings for the circuits, plausible readings for R1 + R2 etc and the RCD trip times....)

So in failing light, I noted that using an upstairs socket would trip the opposite RCD, and activating the cooker circuit would also trip the same opposite RCD.

All the cables in the CU are a mess, a combination of red/black and brown/blue with choc block and joints and changes of colour....

So my Saturday is now going back to "unpick" all the circuits and reconnect them.

What a shambles and to think so twxt of a sparky has left this in such a state makes me dispair!

Rant over.....
 
Be nice to phone the "electrician" who obviously made up these figures and ask him how he manages to sleep at night.
 
I've had the same with an NICEIC registered sparks.

Wasted a morning for two of us because we couldn't do anything with the lighting circuit as it had no CPC. Funny thing was the EIC from the other sparks has Zs reading for this circuit!!

I'm with the NICEiC and I used to be very proud to be registered. Not any more. They just let all kinds of muppets in and it just costs me money all the time.
 
These guys need reporting I shudder to think how many unsafe installs that they are leaving
 
I agree, but who do you report them to?
Nobody really cares, and even the NIC would simply say "They must have a chance to correct it."

I've tried, but the NICEIC say the complaint must come from the customer, else it looks like sour grapes between sparkies!
 
I don't think anyone really gives a damn unless someone gets hurt. Look at the loft insulation fiasco that's ongoing... We have to derate cables unless we keep them out of the yellow stuff, yet BG can come along and dump 2 feet of the stuff straight on top of existing cabling!
 
I've had the same with an NICEIC registered sparks.

Wasted a morning for two of us because we couldn't do anything with the lighting circuit as it had no CPC. Funny thing was the EIC from the other sparks has Zs reading for this circuit!!

I'm with the NICEiC and I used to be very proud to be registered. Not any more. They just let all kinds of muppets in and it just costs me money all the time.

Its a bit like the other discussion with regards to certification in Scotland and some of our LABCs insisting on NICEIC or Select registration but if only people realsied that the LABC and NICEIC dont police the system (Select does) and I have to attach qualification and calibration to the cert yet they just put their NICEIC number and thatss meant to be good enough.

I have come across this too many times from these so called registered people who hide behind a badge and slag off anybody who is not registered I think thats why Joe Public has no confidence it the scheme system as one said how is it I am getting you in to fix it
 
I've found that most customers just take a tradesman's word for it that he is capable and qualified to do a job. The only time I have EVER heard a customer ask about registration is where it involves gas, mainly thanks to programs like watchdog, who cram it down our throats.
 
that's because, down south (or darn sarf, as it's said there) most customers have learnt to reed and rite.
 
Anyone I have spoke to about it hasnt got a clue about it and doesnt realy care as longas the job is cheap as possible and as longas it works they think evrything is fine after explainging the whole part pa nd its nonsense think it sjut leaves them bewildered
I also leave them a leaflet with relevent info I have downloaded from ELECSA and try my best to explain in as simple terms as possible
the NEW part p is due and yet when you try to ask about it the giovering bodies cant tell you whats happening with regard to 3rd party I&T and notifcation
and reducing the number of notifiable jobs will mean any Tom the Plumber, dick the builder or Harry the kitchen fitter can do it and either not have to notify which will mean probably no certificate Or testng carried out or they will do that then get some spark to sign for I&T and sign the JOB off and this costs me MANY ££££££££££££££££££££ each year
 