I'm pretty confident it's TT although haven't metered.
Old meter in still in place.
Same Earth cable leaving box can be seen other side of wall connected to Earth rod.
Concentric incoming cable does not look like a TN-S cable.
I'll meter it before making any big decisions
Will recommend a meter upgrade + check to see if TNC-S is available to remove issue of TT tails not being RCD protected.
In the meantime - will fit limiter to EV charger.
Ok interesting thanks. Explains that.
Not much point in uprating them since the meter is only rated for 80A. Looks like I'll have to get the DNO involved and wait for eternity.
In the meantime, I can fit an import limiter to the EV charger.
Evening,
Carried out EV charger installation survey today & found this meter. Is that a 16mm concentric type cable adapter between cutout & meter?
This is a TT installation, tails unprotected. Not sure about installation method of DNO supply.
I'd like to upgrade tails to 25mm between cutout &...