Recent content by kropaske

  1. kropaske

    G99 GSI-3 4.4 kw Victron inverter install

    Registered capacity is what you set up as export limitation within inverter menu so in your case you should set it at 16A. If you would install 4 inverters, then to use SGI-1 total export on all units should be set at 16A, i.e. 4A on each inverter - so that's fine Here, each new and existing...
  2. kropaske

    G99 GSI-3 4.4 kw Victron inverter install

    In your case I would be looking at G99 SGI-1 procedure which is basically install and notify. Your inverter meets requirements of that as it's less then 32A. Just need to set export limit to 16A within inverter menu.
  3. kropaske

    Optimum setup of 2 strings on Solis RHI hybrid inverter

    It's Sofar hyd 6000 ES https://www.google.com/url?sa=t&source=web&rct=j&opi=89978449&url=https://www.pluginsolar.co.uk/downloads/sofar-hyd-user-manual.pdf&ved=2ahUKEwiTp-f086SCAxVCUkEAHVIFAYMQFnoECCMQAQ&usg=AOvVaw1oEyPedaH8a5wfpYUgcAPj
  4. Screenshot_2023-11-02-08-32-30-223_com.miui.gallery.jpg

    Screenshot_2023-11-02-08-32-30-223_com.miui.gallery.jpg

  5. kropaske

    Optimum setup of 2 strings on Solis RHI hybrid inverter

    @heri1177 I don't have experience with Solis inverter but I run Sofar hybrid inverter with 2 mppt configured in parallel. It's 1 string connected to both mppt channels with Y splitter. This allows to run at full voltage per each channel but half the current
  6. kropaske

    MCS Certification 3rd Party??

    3.6kw is no longer magic figure, in certain cases you can install up to 32A with G98(install and notify) Some kind of transfer switch will be needed to switch between normal feed and EPS feed You can have mcs 3rd party certification, just need to call few companies to get quotes. I enquire...
  7. kropaske

    Who's equipment is this: BNO or DNO

    Yeah, I need to extend 1 circuit. Are there any suitable sheeting/insulation that can be retrofitted to those tails?
  8. Screenshot_2023-10-05-08-40-24-957_com.miui.gallery.jpg

    Screenshot_2023-10-05-08-40-24-957_com.miui.gallery.jpg

  9. Screenshot_2023-10-05-08-40-33-868_com.miui.gallery.jpg

    Screenshot_2023-10-05-08-40-33-868_com.miui.gallery.jpg

  10. kropaske

    Who's equipment is this: BNO or DNO

    So this is 1st floor maisonnette with concrete floor, 16mm2 single insulated tails coming from dual cut out on ground floor, through steel conduit, which is used as earth with some old clamps and bare wires. Tails terminates in another cutout as per pics and then arrangement is as usual. System...
  11. kropaske

    High Ze reading fails EICR

    @pc1966 , @westward10 I take both of you points guys but we only testing on the day and we can't really assume how long this fault was preset, and whether it will get worst in a day or year. We also know that repair is arranged. Whether satisfactory or not, would you leave this installation...
  12. kropaske

    High Ze reading fails EICR

    This is interesting scenario. Seems that DNO are very slow in response to this situation. When I had similar readings on the job they were within couple of hours not months digging outside. But assuming there is relatively new CU with tails nicely glanded and secured and all circuits RCD...
  13. kropaske

    What are the regulations for PV consumer unit protection?

    There is no requirement to install RCD protection to PV system AC cable unless it's required because of installation method as mentioned above, or manufacturer instruction insist on installing one. Looking at MI your system should be protected by 20A OCPD
  14. kropaske

    Polarity on this led driver

    Surely that is not the case. While UK have polarised sockets most EU does not, so any devices with the plug must be designed in such a way to be safe either way they are connected, unless they are hardwired and manual specify how to connect it.
  15. kropaske

    Anyone know this RCD symbol?

    To be more specific shark fin/open door/saw tooth sign means RCD will resist surges 8/20μs up to 250A, Selective type with non operating time of at least 40ms (S) will resist 8/20μs up to 5kA Delayed type with non operating time of at least 10ms (G) will resist 8/20μs up to 3kA

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock