Recent content by norcal

  1. N

    adding a dryer plug

    You cannot extend a existing 3 wire dryer receptacle, it has to be brought up to current code, they are only permitted in existing locations, no extensions or relocation.
  2. N

    Wiring 50amp outlet, but only 3 wires run to the disconnect

    If the feed is NM cable "Romex®" you will need to pull a new cable from panel, if is in pipe it might be possible to add a neutral but might not be easy, just running a neutral by it's self will not be code compliant.
  3. N

    Ground bar neutral bar connection

    The 2023 NEC has only been adopted by 5 States, so unless one is in CO, MA, MN, WY, or TX, might be still a bit premature to quote the 2023, Massachusetts always is first to adopt in the January of the year it comes out.
  4. N

    220v attic conduit question

    Do you have capacity to handle a tankless? Some models require up to 3-40A feeds to supply them, which could mean a upgrade of the service, I hate propane but I would consider it.
  5. N

    Twin and Earth American style

    At one time non metallic sheathed cable commonly known by the brand name "Romex®" formerly made by General Cable, now made by Southwire, had a 16 AWG ground wire in 12 and 14 AWG sizes, sometime after the adoption of the 1968 NEC, it was required that the grounding conductor in 10,12,14, AWG...
  6. N

    What is the age of fuse box.

    General Switch does not exist anymore either, last time I saw their brand for sale is when I stopped in a home center in Texas in early 2000 & saw their panels being on clearance. That fusible panel is old, by the late 1970's fusible panels were removed from the manufacturers catalogs
  7. N

    Why are metal electrical boxes so small (compared to PVC?)

    The old cable was AC, not MC, they each have their own NEC articles, and installation requirements, one difference is AC requires the use of anti short bushings, & MC does not, & older AC cable without a bond strip is not suitable for grounding, in a fault the armor could be glowing red if it is...
  8. N

    Backstabbing: electrician says all outlets in home should be replaced?

    You do realize this this thread dates back to 2020?😀
  9. N

    USA Ceiling Fan Box is Strange

    It would only be required if was prewired for a fan, but a good idea anyway, even if not wired for a fan/light someone will hang one even on a plastic box, bloody tenants hung fans off cut in boxes rated for fixtures 5 pounds max, ticked me off since they had no business messing with the wiring...
  10. N

    Adding a 20 AMP tandem circuit breaker

    Eaton BR is OEM for Challenger, notice the 2 catalog numbers on Eaton BR breakers, BRxxx, & Cxxx, a 20 ampere single pole would be BR120, & C120, the "C" is for Challenger.
  11. N

    10/3 120ft. Black and red On 1 breaker to keep amps up. What is the max breaker for that?

    The NEC does not permit paralleling conductors smaller then 1/0 see NEC article 310.10 (H) (1), which is what is being done, only way to be code compliant is to use larger conductors, and then 250.122(B) kicks in and you have to increase the size of the grounding conductor proportionately in...
  12. N

    French Regs/Signing off French installs?

    For my own personal curiosity, is a ring circuit permitted in France? The comments in post # 8 is why I ask.
  13. N

    DIY - Apartment wrong 4-prong 220v wiring, how to fix myself?

    It looks like the receptacle is miswired, it never should have been changed to 4 wire, as there is no grounding conductor and doofy the wannabe electrician connected the neutral to the grounding terminal, a 3 wire dryer cap is a dual voltage non grounding device, the landlord should have it...
  14. N

    Distributing kitchen appliances between circuits

    The fridge is permitted to be on a kitchen small appliance branch circuit 210.50(B)(1) NEC 2017 edition. Unless working in a area that has amended the NEC to be more stringent.
  15. N

    Compressor wiring question

    110 & 220 volt were obsolete before the 2nd world war, as long as it is not a disconnect it is allowed only break one leg of a 240V circuit, it is quite common in air conditioning condenser units, that being said I would use a 2 pole switch rated for the motors horsepower.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock