Thanks Matt. Agree about IR testing however my point on this post is that the meter is still seeing 0.2A in the earth conductor even when there is no potential between L-N in the whole installation. I suspect there maybe current flowing in the system from the DNO's earth and the installations...
Visible TNS connection looks good (visible bit anyway). Disconnected EC from CU end and zero reading. Measured 0.1A on bonding conductor to gas though. Water not tested yet. Haven't carried out Ze yet (ran out of time) but will do on next visit.
Never experienced before on a domestic - I'm...
Called out today by new owners to a domestic 3 bed semi with history of nuisance RCD tripping from day 1 (lived there about a month). TNS. No dual supply. No regular pattern to tripping. Most appliances new.
First - Ramp Tested RCD unit with no loads = 25mA (can live with that). Popped...
I've had exactly the same problem today.
Called out to domestic 3 bed semi by new owners with history of nuisance RCD tripping from day 1 (lived there about a month). TNS. No regular pattern to tripping and most appliances new. First - Ramp Tested RCD unit with no loads = 25mA (can live with...
Capping (metal or plastic) only protects cables from the plasterers trowel and is not a form of recognised mechanical protection. As long as the cables are in the correct zone and are RCD protected then they are electrically compliant. Not sure about the reg that mentions workmanship tho.
Just completed the NVQ with XS training. Whole thing is very straightforward with their great online portfolio system. David provides great level of support where necessary. Would recommend this training provider to those that need/want this qualification.
Thanks to all at XS, Pete Mills
Sound advice from Archy.
Dont bother with 'Exam Success' books. All the answers are in GN3. There is no substitute for having a thorough working knowledge of its contents. Pay attention to exact terminology, correct sequences and the use of accurate diagrams. The questions need to read carefully...
Also,when replacing a CU, unless there is an existing isolator fitted upstream of the DNO supply arrangements prior to the old CU it is not possible to carry out safe isolation with out breaking the seals, pulling the fuse and proving dead.
IMO,DNO's need to accept that their guidance on the...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc