    no class II markings

    Bit worrying guys are doing the inspection and testing of appliances without a grasp of resistances!!!! Thankfully all at my company are maintenance electricians.
  2. S

    no class II markings

    Your top test results look good, the only thing I would add is running the load test with the power supply plugged into the device and some load on it if possible. Is this the same supply you tested yesterday with the high leakage current? Having a look at the figures underneath I would drop...
  3. S

    no class II markings

    No the reduced voltage IR test is deemed safer for IT equipment and will be fine for your DC power supplies you are currently testing.
  4. S

    no class II markings

    Hubsy, I think the europa does a 250V insulation test, I would be inclined to try that to see what the reading is? It does say in the COP that sometimes due to large capacitors in SMPS's you might get a low reading, maybe try this and see as I would be interested to see the results!
  5. S

    sample form,pat testing from 4th edition required please

    I don't think it is illegal to use the model forms in the COP, not so sure about distributing them though?
  6. S

    pat testing documentation

    Lorna Thanks for the reply, the changes you are talking about are what I was looking for. I am basically looking for software that would record each process as designated in the COP for the formal visual checks when they are made. Please keep me informed on its progress!
  7. S

    no class II markings

    Hubsy Looking at the figures you have above technically the power supply would fail on the leakage test. Page 96 of the cop has the leakage values and as the charger would be portable it would fail as over the limit of 0.75mA. What do you all think? What tester are you using, I would be...
  8. S

    no class II markings

    What is the scanning equipment you are on about, what does it do does the scanner dock with the base station to charge? I personally wouldn't check the base station as it is 12V DC or the scanner as it must be a 12V battery?
  9. S

    sample form,pat testing from 4th edition required please

    Good luck with that my firm thankfully bought the books although I had my own copy anyway. No t too bad after I had pointed out the company they had in doing the testing were clowns which has been proven with some of the faults we have found and no fixed testing by them also!!!
  10. S

    pat testing documentation

    Thanks for the reply! Sorry to pester you again but say for arguments sake you are adding a lead to the program with a visual frequency of 6 months and a combined inspection of 12 months. Would you create the asset in the program with a six month testing frequency then fill in the relevant test...
  11. S

    no class II markings

    I would still test it as a class 1 item, is there a DC jack you can run a 200mA earth continuity test on sometimes you will get continuity on the end of the jack.. If not then I would mark it as no accessible earthed parts then IR test it as normal. I have a dell charger and can definitely get...
  12. S

    pat testing documentation

    Quick question for the SimplyPat's users on here, does the program keep a history of an appliances test results for you to look back at?
  13. S

    sample form,pat testing from 4th edition required please

    What is it your looking for as there are are other changes in the fourth edition other than the test form? From memory the test form has a new layout to the third edition one but I would need to dig out my third edition book which has been long ditched to see the exact changes!!
  14. S

    Fuse Size

    In the case above a manufacturer flex of 0.75 should have a moulded plug fitted and should have a length under 2M and this is allowed to be fused at 13A under BS1363
  15. S

    Pat testing

    You will need to know firstly the size of cable and length used to supply the appliance to calculate the resistance of the cpc. The other option is to measure the resistance of the cpc of the length cant be accurately determined. As the other guys have said when testing the fixed appliance the...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Advert

Back
Top