Replacing Fluorescent batten with LED

I have a fluorescent light "tube" light in a kitchen that I want to replace with a LED light

There are 5 wires coming out of the ceiling connected to the Live Earth and Neutral on the fitting.

The new LED light I have purchased is plastic so does not need an earth.
I put the Earth wire in a connector and taped it up.

This leaves 4 wires,
1 Red and 3 Black (1980s wiring).

Two combination of black connected to the new LED allow other downstairs light to work, without then in the LED neutral connector they do not work,
I assume they are are both neutral.

I though the red was permanent live, but it appears to be a switching live. I put that in the LED and it works as do all other downstairs lights,
However, one landing light controlled by 2 switches does not work.

That leaves one black cable. This appears to be a permanent live. If I put it in with the red wire in the LED light the upstairs light works, But switching it on puts the kitchen LED on dim and it will overload. The black live has been taken out and isolated. This seems to indicate it is a permanent live and needs to be connected to supply power to the upstairs light.

If I connect the red and black live together (outside the LED) and move one black neutral to the LED nothing works, If I swap the black neutrals nothing works. This implies both are neutrals.

It seems the old fitting had both red and black live connected together. The batten could handle this poor installation and the ballast requirement did not switch it on if the landing light was switched on.

I suspect I need an electrician to connect this black live to a live to complete a circuit to the landing light. This is not a job for me.

My questions:

1. Is my analysis of the wiring correct, or have I done something wrong and there is a simple solution and simple connections?
2. Do I indeed need the black live to be connected to a live for the upstairs light for it to work, by an electrician? Not something I would attempt.
What exactly do I tell an electrician I want doing? Currently the black live is isolated and the landing light does not work.
3. Are there any LED devices that could be used that have a loop or connectors that would resolve my with simple wiring in (I assume a ceiling rose pendant would - but I do not want that).

Any other advice?

Thanks.
 
Looking at the wiring I can only surmise all three blacks need to connect to neutral together and the red into live.
 
Looking at the wiring I can only surmise all three blacks need to connect to neutral together and the red into live.
May I ask why you say so?

But the third black appears a live and when I put it in live it gives power upstairs and then overloads the LED after a while.

Is it really a third neutral? Is that was you are assuming?

If it is live will it cause a short, wouldn't that be putting it into the neutral terminal means you are connecting a Live path directly into a Neutral path?
 
I am only assuming based on the type of wiring that being not multicore cables where a black could be a live. Your's are single wires and the blacks are almost certainly neutrals, the fact one is indicating live may well be due to the return from another light. Do you have any other lights which are easy to look in?
 
I am only assuming based on the type of wiring that being not multicore cables where a black could be a live. Your's are single wires and the blacks are almost certainly neutrals, the fact one is indicating live may well be due to the return from another light. Do you have any other lights which are easy to look in?

But what about my The Upstairs Light Test? When I put that third black wire into the Live terminal with the Red wire, the upstairs light fully worked. If that black wire were a neutral picking up a faint "stray return voltage," would it really have the power to illuminate the upstairs light? It also powered the kitchen LED dim. Doesn't this indicate a live?
 
Maybe should have taken a photo of the old light connections before disconnecting.


If we are sure the red is coming from the switch, then blacks can only be one of two things… another live, or a neutral.

Unfortunately, randomly connecting things together will eventually cross a live and neutral, resulting in, at least, a tripped circuit breaker which may now need replaced.

the fact that the red is turned over suggests it was the only cable in one connector… the 3 blacks are single… so all together?


When you say it “overloads the LED” with what you are trying…. Do you mean it’s tripping off the breaker?
 
Best you call an electrician.
Electriciantools
Electriciantools
Maybe should have taken a photo of the old light connections before disconnecting.


If we are sure the red is coming from the switch, then blacks can only be one of two things… another live, or a neutral.

Unfortunately, randomly connecting things together will eventually cross a live and neutral, resulting in, at least, a tripped circuit breaker which may now need replaced.

the fact that the red is turned over suggests it was the only cable in one connector… the 3 blacks are single… so all together?


When you say it “overloads the LED” with what you are trying…. Do you mean it’s tripping off the breaker?

Maybe should have taken a photo of the old light connections before disconnecting.


If we are sure the red is coming from the switch, then blacks can only be one of two things… another live, or a neutral.

Unfortunately, randomly connecting things together will eventually cross a live and neutral, resulting in, at least, a tripped circuit breaker which may now need replaced.

the fact that the red is turned over suggests it was the only cable in one connector… the 3 blacks are single… so all together?


When you say it “overloads the LED” with what you are trying…. Do you mean it’s tripping off the breaker?

Maybe should have taken a photo of the old light connections before disconnecting.
==> Yes, But a cable came lose when pulling.

If we are sure the red is coming from the switch, then blacks can only be one of two things… another live, or a neutral.
==> Red in LED the light works fine from 2 switches

Unfortunately, randomly connecting things together will eventually cross a live and neutral, resulting in, at least, a tripped circuit breaker which may now need replaced.

the fact that the red is turned over suggests it was the only cable in one connector… the 3 blacks are single… so all together?


When you say it “overloads the LED” with what you are trying…. Do you mean it’s tripping off the breaker?

Maybe should have taken a photo of the old light connections before disconnecting.


If we are sure the red is coming from the switch, then blacks can only be one of two things… another live, or a neutral.

Unfortunately, randomly connecting things together will eventually cross a live and neutral, resulting in, at least, a tripped circuit breaker which may now need replaced.

the fact that the red is turned over suggests it was the only cable in one connector… the 3 blacks are single… so all together?


When you say it “overloads the LED” with what you are trying…. Do you mean it’s tripping off the breaker?

One wire came out when pulled out.
Red in Live LED - light works perfectly from 2 switches === seems switched live
Two blacks in neutral allows other downstairs lights to work, without them they will not.
Last black in live with red allows upstairs landing light to work, but the switching on makes LED dim when off and then after a while all lights off. DOd not occur with old batten (needed ballast). Hence, seems live - power to upstairs. Isolated and now light in landing not working.

All others lights work correctly.

Time for electrician!
 
I am only assuming based on the type of wiring that being not multicore cables where a black could be a live. Your's are single wires and the blacks are almost certainly neutrals, the fact one is indicating live may well be due to the return from another light. Do you have any other lights which are easy to look in?
Correct it was a neutral.

The electrician was confused. One showed a 230V and another 130V. I suggested he look at wiring in the next room which when inspected had 3 neutrals. That too was swapped for an LED. Well over 30 mins procrastination before connection. I guess 7-years experience was not enough for a quick decision.

When I put 3 neutrals together in the terminal the connection must not have been made correctly.

Anyway, I got him to change 3 more fittings at the same time.
All solved.

Thanks for the advice.
 
Thanks for the update I guess my surmising from 40+ years experience was ultimately correct 😃
 