What a beautiful meter room!

HappyHippyDad

~
Arms
Supporter
I rarely seem to work in flats, so don't get to see many meter rooms, but I don't remember seeing any as neat as this!

It looks like a work of art.

meter room1.webp



meter room2.webp
 
Indeed, rare to find a tidy job like that.
My first thought was "wait till a few sparkies and meter fitters have had a go", then I noticed they already have, and the tails are definitely no longer as neat bottom right of the first photo.
Also, isn't there a lack of mechanical support ? Those vertical runs (except perhaps the far back wall) seem to be supported by cable ties to each other, with everything supported on the terminations.
 
Do you think they allowed for Grouping Factors?? 🤣
 
16mm T&E for risers out of them switchfuses or is it tails over 3 meters. All cabling just strapped with plastic cable ties on that tray. ( not compliant in todays standards) But yes neat.
 
I don't think I'll put another nice picture up :D :D
 
What's wrong with that if it has the right rating relative to fuse size.

I don't see any of that.
Well just to answer your question regarding using 16mm T&E for a distribution cable is the lack of mechanical protection, it is likely to be traveling through the fabric of the building less than <50mm depth with no RCD, obviously we dont know this by looking at a picture nor how can it be proven only on initial verification.
I think those are tails coming out of them switch fuses which are clearly over the 3meter rule mark, you must agree with me about the support of them cables because you didnt mention it, in the event of fire those horizontals runs will just be tangled round any firemans earholes because of lack of mechanical support.
 
Well just to answer your question regarding using 16mm T&E for a distribution cable is the lack of mechanical protection, it is likely to be traveling through the fabric of the building less than <50mm depth with no RCD, obviously we dont know this by looking at a picture nor how can it be proven only on initial verification.
I think those are tails coming out of them switch fuses which are clearly over the 3meter rule mark, you must agree with me about the support of them cables because you didnt mention it, in the event of fire those horizontals runs will just be tangled round any firemans earholes because of lack of mechanical support.
Apart from all that though Dave, It's still pretty :D
 

OFFICIAL SPONSORS

Back
Top