  1. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    IET Forums - Fuseboard Change with no cpc in lighting - https://www.----------/forums/forum/messageview.cfm?catid=205&threadid=64580
  2. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    I can't find original if I do I will get it to you, plus it's a Saturday.
  3. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    Mate I have not got that link but I just found this. Lighting circuits with no Earth (CPC) - Electrician Swindon | Electrical Testing & Inspection Swindon - http://www.crannistech.co.uk/lighting/
  4. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    Sorry I mean that you can not change them to plastic anymore or advise that they cannot ever be replaced for metal. But now under 18th all must be CPC.
  5. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    The definition of the codes used on eicr are not changing, and neither are the requirements for cpcs. This issue will be no different on a periodic inspection in the 18th to what it is now. I was reading an IET mag about changes in the 18th, there was a section about CPC to lighting, it's a...
  6. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    The definition of the codes used on eicr are not changing, and neither are the requirements for cpcs. This issue will be no different on a periodic inspection in the 18th to what it is now. I was reading an IET mag about changes in the 18th, there was a section about CPC to lighting, it's a...
  7. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    What is changing? You cannot report it as an c3 and advise no metal fixtures, there has to be a CPC connected.
  8. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    From Electrical Safety First However, circuits that are defective or non- compliant with the requirements of BS 7671 in a way that would result in immediate or potential danger must not be reconnected to the consumer unit.
  9. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    But I'm sure you can not change a fuse board if earthing not correct. It defeats the object. If an inspector asks you to carry out an RCD trip test, you are in trouble
  10. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    Exactly, there can not be any C1 or C2, otherwise he cannot issue an EIC. All has to be earthed and all mcbs and RCDs need to meet the requirements of the regs. I will never issue a EIC knowing that's the earthing to the lighting is not in place and I will tell Mrs Jones, I cannot continue with...
  11. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    If there is no R1 + R2, it's pointless to have an RCD. Earth continuity, is a must. RCDs are for earth faults. You tell Mrs Jones that you replaced her board with an up to date version but will not have the benefits of a new version, but it's fire protected because it's metal. Might as well...
  12. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    Regs, looking at old certs dated 2013 and then phoning up and asking the person issuing the certs that he passed an periodic inspection even though there is no earth to lighting. I always believed with my old company that you had to earth no matter what. Apparently you could get away without CPC...
  13. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.
  14. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.
  15. sham

    No cpc on lighting and no neutral continuity on kitchen ring

    The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.