Too right I'm confused. The question isn't specifically about SWA but taking that as an example, if there were a phase to armour fault that would be picked up even if the armour were not connected to earth.
Much appreciate your answers so far but I don't feel anyone has actually given a compelling reason (other than the regs which I already quoted in the OP).
A question for testers to settle a debate at work - GN3 & regulation 612.3.1 state that when doing insulation resistance, the CPC/armour of swa MUST be connected to Earth.
Does anyone know why this is please?