A question for testers to settle a debate at work - GN3 & regulation 612.3.1 state that when doing insulation resistance, the CPC/armour of swa MUST be connected to Earth.
Does anyone know why this is please?
 
in case the cable is damaged .........

when IR testing, all CPC's should be connected to the earth bar!
 
Because the IR test is between line and CPC/earth - if the CPC isn't connected to anything then you could have a short between line and CPC/earth which the test wouldn't identify.
 
By completing the R1+R2 testing at each point on the circuit during initial verification you are confirming the cpc is continuous and present then you can move on to IR testing , assured that the cpc’s will be included in the test and is not discontinued to give the tester false or incorrect readings.
There is a reason that the testing sequence in initial verification is there and it’s worth remembering that any issues found during IR may mean you have to repeat the previous tests.
 
When you say the cpc / armour connected to earth are you just referring to swa cables and how would it not be connected to earth if glanded to a metal enclosure.
 
It has been explained but you don't seem to have understood.

You have to have a CPC for the IR test to work.
You need to test the CPC before you do any other test that needs the CPC.

It's like making sure your tester works and your leads aren't broken before you start testing.
 
It's the same idea - if the live is making contact with the armour then an IR test will show that up unless the armour isn't earthed, in which case it'll just liven up the armour to 500v. The test might show you have a high resistance, but then when you energise the circuit the armour will become live.
 
Yes I know but have they installed these cables with no earth to the armour.
 
Perhaps the op is getting a little confused and is referring to the requirement to discharge the conductors of an swa to earth following an insulation resistance test. I could be barking up the wrong tree though.
 
Too right I'm confused. The question isn't specifically about SWA but taking that as an example, if there were a phase to armour fault that would be picked up even if the armour were not connected to earth.
 
When you say the cpc / armour connected to earth are you just referring to swa cables and how would it not be connected to earth if glanded to a metal enclosure.
Might not be a very good termination, judging by some I have seen,
 
However if there was a fault from a live conductor to another piece or earthed metal nearby the test from armour to live conductor woudl show as OK.
If the armour was connected to the earthing system then the short would be shown on the test result.

View attachment 41916
excellent explanation.
 
Too right I'm confused. The question isn't specifically about SWA but taking that as an example, if there were a phase to armour fault that would be picked up even if the armour were not connected to earth.

OK,so if you expand this notion to any other cable,the reasons for earthing that particular conductor,during that particular test,are obvious.

Another reason,if one was needed,for earthing the armour on SWA during an IR test,would be that even if the armour only provided mechanical protection,an indication of it's integrity,that is to say,how the outer sheath may be providing prevention of moisture,rust,etc,in relation to the environment (earth) is also tested.

I still have not heard the counter debate,from the OP,of why the other side of this argument,feel it is not necessary...
 
OK,so if you expand this notion to any other cable,the reasons for earthing that particular conductor,during that particular test,are obvious.

Another reason,if one was needed,for earthing the armour on SWA during an IR test,would be that even if the armour only provided mechanical protection,an indication of it's integrity,that is to say,how the outer sheath may be providing prevention of moisture,rust,etc,in relation to the environment (earth) is also tested.

I still have not heard the counter debate,from the OP,of why the other side of this argument,feel it is not necessary...

A sadly large number of sparks I have worked with have little respect for the regs. I do not share their views. As this became a requirement relatively recently, 10 years ago, perhaps some people have not kept up with the changes and do not see the importance of it. Let's say that and give them the benefit of the doubt.
 
I draw them out, lines, shapes, connectors, etc.
This one is a bit odd in that it was done quickly and it is hard to indicate a bonding strap on a pipe, but I should have just done another tube inset, nope that does not work either.
I now have a very odd library of very odd diagrams.:rolleyes:

I was wondering Richard,if you could do a family portrait for me?

I could send you a photograph,or,just watch the Deliverance,and sketch two adults and two kids...it'll be near enough...:)
 
As I understand it, apart from other paralell faults, you want the "biggest bang" (PEFC) figure.
 
A question for testers to settle a debate at work - GN3 & regulation 612.3.1 state that when doing insulation resistance, the CPC/armour of swa MUST be connected to Earth.
Does anyone know why this is please?
I have just read this post and was so shocked I have had to put my Cider down and take a walk up the garden, I am in total shock to be honest, what on earth are they teaching you Kids these days, time to stick my head in a bucket of water, clearly the cider is making me confused lol
 
A question for testers to settle a debate at work - GN3 & regulation 612.3.1 state that when doing insulation resistance, the CPC/armour of swa MUST be connected to Earth.
Does anyone know why this is please?
I have just read this post and was so shocked I have had to put my Cider down and take a walk up the garden, I am in total shock to be honest, what on earth are they teaching you Kids these days, time to stick my head in a bucket of water, clearly the cider is making me confused lol
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
cambridge

Thread Information

Title
Why Earth before IR testing?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
32

Thread Tags

Advert

Thread statistics

Created
Woofie,
Last reply from
MDJ,
Replies
32
Views
5,790

Advert

Back
Top