Hi, would like ta post a question about voltage drop in a cable. If I have a 230v single phase load of 500w with a 50 meter cable run reference method C . What would be the voltage drop in a 1.5mm2 ? From my calculations excluding pf I checked from the table the the voltage drop in mV/A/m of a...
Just after a bit of advice from thoose of you that deal with this regularly & want to make sure i get it right.
Swa submain to phone network mast
63Amp single phase supply
Pme supply assumed ze of 0.35
245M run
Ive been trying to calculate which size swa & cpc or 3c swa to go for, would like...
Evening,
Just joined upto this forum after a search online for some info, hopefully someone can help me?
I have taken over a job from another contractor who has run in a 50mm 4 core swa from a substation to a TP&N DB roughly 100m away.
My concern is that it appears they have not run a separate...
If possible could anyone have a quick look over these steps I've made myself for cable sizing and the protection needed. Please let me know if I've missed out anything.
I also couldn't find a definitive answer for maximum permitted voltage drop percentage for 3 phase. I think it was 5% and 8%...
Hello everyone,
I would like it if anyone would be able to help me in listing the steps For choosing cable size.
Starting from protective device from a boards 'Zs' value, all the way to the cable size.
Thanks in advance
Hi,
Can anyone point me in the direction of the regulation / code for the max solar MCB size when connecting into a spare way of a local distribution board ?
Eg. Is it possible to connect a 100A breaker into a 100A board ?
Stengs
Thread
breaker
distribution board
maximum
mcb
size
solar pv
three phase
Hi guys, I've been given the task of installing a 32A commando socket w/ isolator, which will have a 27A oven plugged into it. It will be on a C32 30mA RCBO. The cable from the oven is 4mm which will have the 32a commando plug fitted to it.
My question is, should I wire the 32A commando socket...
Now I completely understand why cables must be fused down when a lower size cable is connected to a larger sized cable. To ensure the cable does not burn out from current that it cannot take.
Yes i know this
Now current doesnt go anywhere it isnt in demand for so if a spur off of say a 6mm for...
Looking through our periodic certificate that was completed by a 3rd party, I've got a few queries that hopefully someone on here can clarify.
We've got a Schneider Prisma switchboard (S3/MSP 3.1) fed from 11kV/400V Transformer.
- What is meant by MW for cpc size of 2/TP and 13/TP?
- Is there...