ukpablo

hi

have just qualified 2330 level and purchased a megger 1553. Im happy with all of the test procedures but could somebody please help explain the two wire method for rcd testing at the board with the 1553.

I have the setting on no trip, option 1 two wire method from instructions, does the green probe go to the cpc and the red probe on the phase of the rcd cct? its the green cable thats confusing me and why is the black probe not used?

also pfc measurement?

where the leads go and what option to use? all to be done at the cu.

thanks
pw:mad:
 
thanks
that clears that up. red to phase, black to n and green to cpc! makes sense.

any ideas on pscc, pefc and pfc

is pscc:

red to phase
black to n

pefc:

red to phase
black to n
green to cpc

then record highest as pfc?

thanks
 
Have a look on you tube, you might find what you want.
[ame=http://www.youtube.com/watch?v=PniIhehMNf8]YouTube - Megger MFT1552 & MFT1553 Demo Part 1[/ame]
 