Hi

Can any one point me in the right direction Re literature or articles concerning 3 lead method of testing .
The limited testing i have done & DVD's only seem to have used 2 lead methods .Any advice would be
appreciated.

Thank you in advance

Angus
 
The only time you need 3 leads on the megger is on the no trip Zs setting and the RCD setting. All other tests including Zs and pfc on the high current setting need only 2 leads.
 