I rarely seem to work in flats, so don't get to see many meter rooms, but I don't remember seeing any as neat as this!
It looks like a work of art.
It looks like a work of art.

What's wrong with that if it has the right rating relative to fuse size.16mm T&E for risers out of them switchfuses
I don't see any of that.or is it tails over 3 meters
Well just to answer your question regarding using 16mm T&E for a distribution cable is the lack of mechanical protection, it is likely to be traveling through the fabric of the building less than <50mm depth with no RCD, obviously we dont know this by looking at a picture nor how can it be proven only on initial verification.What's wrong with that if it has the right rating relative to fuse size.
I don't see any of that.
Apart from all that though Dave, It's still prettyWell just to answer your question regarding using 16mm T&E for a distribution cable is the lack of mechanical protection, it is likely to be traveling through the fabric of the building less than <50mm depth with no RCD, obviously we dont know this by looking at a picture nor how can it be proven only on initial verification.
I think those are tails coming out of them switch fuses which are clearly over the 3meter rule mark, you must agree with me about the support of them cables because you didnt mention it, in the event of fire those horizontals runs will just be tangled round any firemans earholes because of lack of mechanical support.

YupApart from all that though Dave, It's still pretty![]()

That's an assumption. It may well be going up a service riser and not in a position where it needs additional protection by RCD.Well just to answer your question regarding using 16mm T&E for a distribution cable is the lack of mechanical protection, it is likely to be traveling through the fabric of the building less than <50mm depth with no RCD, obviously we dont know this by looking at a picture nor how can it be proven only on initial verification.
I don't see it. If I had to guess, I'd say I don't see anything over about 2m.I think those are tails coming out of them switch fuses which are clearly over the 3meter rule mark
Yeah, sort of. Would they be going in there rather than spraying mist from the doorway ?you must agree with me about the support of them cables because you didnt mention it, in the event of fire those horizontals runs will just be tangled round any firemans earholes because of lack of mechanical support.
Really, I would say the next stop would be in the back of the CU. In the apartments/flats.That's an assumption. It may well be going up a service riser and not in a position where it needs additional protection by RCD.
The same would also apply to the 6181Y distribution cables.
I don't see it. If I had to guess, I'd say I don't see anything over about 2m.
One thing I don't like (you can see it clearly on the switch-fuses nearest on the right) is the way they've run L & N tails apart - N goes one side of the switch-fuses below, the L goes the other side.
Yeah, sort of. Would they be going in there rather than spraying mist from the doorway ?
You do have a point that what we see here is probably continued elsewhere.
Lastly, there's a bunch of small cables top right of the first photo. They look a bit like network cables which should really be segregated from power cables.
Oooo theres something a bit Stranger Things about that room but I do like it!I rarely seem to work in flats, so don't get to see many meter rooms, but I don't remember seeing any as neat as this!
It looks like a work of art.
View attachment 125327
View attachment 125328