Hi, DIY'er here. I'Ve purchased new oven which is 2.4kw. Comes with a plug fitted with 13amp fuse. Previous was hardwired into an unswitched fused spur which had a 13amp fuse in. There is a red isolator switch above worktop. It's a dedicated cooker circuit with nothing else on it. Circuit has B32 breaker on consumer unit. Can I just replace the unswitched fused spur with an unswitched single socket to plug in new oven? Or alternatively, the cable from old oven is still attached to fused spur...could I attach single socket to that to plug in oven or would it be an issue having fuse in plug and fuse in spur. Is one way better than the other. Thank you.
 
In a word, yes and no.... Yes you can swap to a 13a socket outlet because the manufacturers fitted plug still has a 13a fuse in it, so there's the protection. No, because an argument could be made that there's insufficient protection from a B32 to a single 13A socket (usually nominally rated at around 19A), irrespective of what's plugged into it, and cable sizing (would need to be at least 4mm) effects that also. A way around both the above would be to swap the B32 for a B20 - however - it could then be argued that you've fundamentally changed the characteristics of a circuit which then makes it a notifiable work.

Choice is yours, but I wouldn't sweat it either way.
 
In a word, yes and no.... Yes you can swap to a 13a socket outlet because the manufacturers fitted plug still has a 13a fuse in it, so there's the protection. No, because an argument could be made that there's insufficient protection from a B32 to a single 13A socket (usually nominally rated at around 19A), irrespective of what's plugged into it, and cable sizing (would need to be at least 4mm) effects that also. A way around both the above would be to swap the B32 for a B20 - however - it could then be argued that you've fundamentally changed the characteristics of a circuit which then makes it a notifiable work.

Choice is yours, but I wouldn't sweat it either way.
It has a 13A plug fitted.
 
Thanks for your replies. So if I change the fused spur to a standard single unswitched socket and downgrade the breaker on the consumer unit to a B16, does that sound like a reasonable course of action?
 

OFFICIAL SPONSORS

Back
Top