Sooo, thought i would give you guys a bit of an update.
All connected but the EL is too high at the DB (0.8 ish) and should be 0.51 for an 80A so i am going back to install and earth rod which should bring it down a fair bit.
I hope!
I dont think an earth road at the intake end is going to be that successful in bringing those readings down, so I guess my only option is to install a TD Rcd before the 80a TPN switch fuse to protect the sub main, and rod the workshop end.