So, it has been flagged that I have a external earth loop impedance of .54 with TNCS earthing and a 100 amp fuse. Advice is to speak to DNO. UK power networks publish that the max is .35.

What are the chances that if I call UK Power Networks to tell them about this they will just bung a 60 amp fuse in there and call it a job well done (as opposed to actually some how lowering the impedence)? That would be sub-optimal, especially given I have RCDs an induction hob and will one day get an electric car and possibly electric boiler!
 
That shouldn't happen as the overall demand / CPD of the installation isn't changing and won't make a bit of difference to youe ELI anyway.

It's probably nothing worse than a loose connection - either way, it's their fault to resolve and is potentially dangerous left as it is.
 
That shouldn't happen as the overall demand / CPD of the installation isn't changing and won't make a bit of difference to youe ELI anyway.

It's probably nothing worse than a loose connection - either way, it's their fault to resolve and is potentially dangerous left as it is.
Thanks - my understanding was that the high impedence coud prevent enough current flowing in an LE fault to cause the 100a fuse to blow in a reasonable period of time. My worry is just that the most cost effective option from their perspective is to say ‘ok- we will derate your fuse’…
 
They’ll repair it, as mentioned above putting a smaller fuse in won’t reduce the Ze reading…
Thanks - my worry was that they had a higher acceptable impedence where there is a smaller fuse (which would be consistent with BS7671 (even though that technically doesn’t apply to them). Repair would be great, except if it involves pulling up my floorboards and digging up my drive to run a new supply cable! 🥵🥵
 
Thanks - my worry was that they had a higher acceptable impedence where there is a smaller fuse (which would be consistent with BS7671 (even though that technically doesn’t apply to them). Repair would be great, except if it involves pulling up my floorboards and digging up my drive to run a new supply cable! 🥵🥵
Sounds like they problem it’s they equipment 😉
 
Thanks - my worry was that they had a higher acceptable impedence where there is a smaller fuse (which would be consistent with BS7671 (even though that technically doesn’t apply to them). Repair would be great, except if it involves pulling up my floorboards and digging up my drive to run a new supply cable
its either sorting it out or a fuse down road jobby .
 
Personally I'd have tested "my end" of it, and also compared it to the L-N reading to give some sense of whether the issue is in the cut-out or not.
There is also an outside chance someone ticked the wrong earthing type box two years ago. I presume you / the sparks is sure it's TNCS.

Legally speaking if UKPN supply an earth it has so be "suitable" and they have to maintain it. From what I understand there is no 0.35 hard limit for the DNO to comply with according to their own policies.
So they may
a) disagree with the reading
b) declare "it's fine"
c) find a loose connection in the cut-out and fix it
d) find an issue further away and fix it
e) fit an up front RCD (it's been known)
f) try and make it your problem and run away

Let us know the outcome, it will be interesting.
 
Personally I'd have tested "my end" of it, and also compared it to the L-N reading to give some sense of whether the issue is in the cut-out or not.
There is also an outside chance someone ticked the wrong earthing type box two years ago. I presume you / the sparks is sure it's TNCS.

Legally speaking if UKPN supply an earth it has so be "suitable" and they have to maintain it. From what I understand there is no 0.35 hard limit for the DNO to comply with according to their own policies.
So they may
a) disagree with the reading
b) declare "it's fine"
c) find a loose connection in the cut-out and fix it
d) find an issue further away and fix it
e) fit an up front RCD (it's been known)
f) try and make it your problem and run away

Let us know the outcome, it will be interesting.
Thanks - that’s helpful. Will update after it’s been sorted.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London

Thread Information

Title
.54 ohm tncs impedemce
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
David Thomas,
Last reply from
David Thomas,
Replies
15
Views
1,375

Advert

Back
Top