I need to install a cu which is over 3m from a new PME supply. Have searched but can't seem to find any 'best practice' advise on what cable to use etc. The cu is 5 meters away. Whats best method?? Is there detailed info on this situation anywhere?

Thanks,

Myles
 
I need to install a cu which is over 3m from a new PME supply. Have searched but can't seem to find any 'best practice' advise on what cable to use etc. The cu is 5 meters away. Whats best method?? Is there detailed info on this situation anywhere?

Thanks,

Myles
you will normally find that the supply authority will require a switch fuse spur as their fuse is only to protect the first 3 m
 
As above reply, install a fused main isolating switch at the mains intake if the board is remote (more than 3 m)
from the consumer unit.
 