T

Tiger

Bought at chrismas impulse buy because it was so cheap advertised as a 17th addition Cu Pack.

wylex 10 way dbl rcd board with 8 mcb's and 10 dbl sockets bargin @ £98 + 15% off:D

went to install it on fri, No probs with the board all the sockets only have 1 earth terminal. New it was to good to be true:D
 
Got to say I think everything is expensive at B&Q for electrical componets.

I only ever use the place if I need something quick (usually small) for a job and it is closer then the wholesaler. Otherwise the wholsalers get my business.
 
because it was a 16th edition requirement that double socket faces have 2 earth terminals and you terminate 1 cpc in each of them
 
Is this true? Where does it state this in current regs?
Darren
 
was this only relevant if there is a possibility of a high leakage current present in the cpc i.e from IT equipment with switch mode power supplies in excess of ( if I recall correctly) 10mA is present ??
 
I havent heard of that 17th regulation either, So what do you do if you have a ring socket feeding a spur and you have 3 earth conductors ?? what do you do then if you can only put 1 in each terminal ?
 
was this only relevant if there is a possibility of a high leakage current present in the cpc i.e from IT equipment with switch mode power supplies in excess of ( if I recall correctly) 10mA is present ??

Spoke to an inspector today and you are correct i must of miss understood him, this is only for I.T systems earth leakage,i terminal in each. also what i did not know is that if you have a radial serving an it system then you must return the cpc like a ring
 

Reply to B & Q Bargin in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

So my old client asked me to look at the eicr and quote he had done on 1 bed rented property to see if i can sort it. It looked like one of those...
Replies
8
Views
2K
I'm trying to design a complete rewire for House of Multiple Occupancy (HMO), but going round in circles as there seems to be endless...
Replies
31
Views
4K
G
Hi all looking for some advice on a job I am doing wiring up the heater of an outside swimming pool.....the heater is 12kw rated 230_v...the pool...
Replies
5
Views
1K
Simple job to add an extra socket to top floor 'rfc'. Top floor was converted some 8-10 years ago but no certs available. Took Zs from socket I...
Replies
14
Views
2K
mickys86
M
Holiday let sleeping 8+. Gas ch (combi) and cooking. 2 x Wylex rewireable cu's, pme (6mm earthing conductor!), no rcd protection. 16mm dno supply...
Replies
27
Views
4K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock