What is the OCPD for the main cable and its size?

I presume it comes from either a MCCB board or some switched-fuse off the DNO cut-out / meter arrangement but knowing the above would allow you to verify it is OK for max current in either direction (load or generate).
 
That existing 250A switch disconnector will have 6mm bolt terminals which will accept two lugs for parallel supplies, not ideal but there is no reason you cannot come direct from it.
 

Attachments

  • 722CA83D-A904-43D1-92E3-EB71AC72D1F9.jpeg
    722CA83D-A904-43D1-92E3-EB71AC72D1F9.jpeg
    461.3 KB · Views: 73
I followed ya advice see attachment but having attempted to double bolt the incomer with my feed cable found there wasn’t the room for both bolts really short see pic above
So looks like a jo go
Any thoughts and ideas would be really welcome to make this happen thanks guys
 