Can anyone help me with anything about this Square D board please? It - and one connected one above, covering only lights - are in a very large house that is mainly early 1990s. If there are any older bits they are well hidden.
I was called out because the main RCD had tripped, taking everything out. It had been reset, but owner couldn't get outside stuff back on again. That was because there was a 30mA RCD between this board and the outside stuff - pumps, fountains in ponds, outside lights, etc.
Once I'd done IR test on outside side and reset 30mA RCD all back to normal.
I'm assuming because 30mA RCD had tripped that circuit is protects was source of fault, and this was big enough leakage current to take out the main board RCD. Whatever that problem was, it is no longer showing up as an IR fault.
So, here's the thing: I was really surprised when I took cover off main board and found the main switch is a 300mA RCD. Everything else is on standard MCB. So if main switch goes, everything goes.
Does anyone know anything about this model of Square D - such as: would it have been installed in early 1990s? It seems way to old for that - maybe that was in 1990s, or maybe it was 're-cycled' from any earlier part of property on that site.
Why a 300mA RCD - not a 30mA - or at least a 100mA? It's a TN-S system, btw.

I was called out because the main RCD had tripped, taking everything out. It had been reset, but owner couldn't get outside stuff back on again. That was because there was a 30mA RCD between this board and the outside stuff - pumps, fountains in ponds, outside lights, etc.
Once I'd done IR test on outside side and reset 30mA RCD all back to normal.
I'm assuming because 30mA RCD had tripped that circuit is protects was source of fault, and this was big enough leakage current to take out the main board RCD. Whatever that problem was, it is no longer showing up as an IR fault.
So, here's the thing: I was really surprised when I took cover off main board and found the main switch is a 300mA RCD. Everything else is on standard MCB. So if main switch goes, everything goes.
Does anyone know anything about this model of Square D - such as: would it have been installed in early 1990s? It seems way to old for that - maybe that was in 1990s, or maybe it was 're-cycled' from any earlier part of property on that site.
Why a 300mA RCD - not a 30mA - or at least a 100mA? It's a TN-S system, btw.