Morning Guys

Anyone else get fed up with plumbers/ builders supplying UFH (wet & electric) gear and it's the cheapest load of cr@p !!
Had enough of tiny little wiring centres/ need microscope to read terminals and stats that take degree to set up.
If it was up to me would only be Heatmiser/ Neo stat all day long.
Moan over now 😉


This weeks surprise looks like it's come out of a cracker 🤣
Anyone had there pleasure of fitting one of these ?
Both units fitted come up with error code ER2, googled it and looks like 'floor sensor broken'.... we're not using floor sensors.
Manual that comes with it is totally incomprehensible.
Wiring from stat to manifold all good have proved.

Cheers Sy
 

Attachments

  • 2ded46de-dc8c-42f2-8650-0a9930dced94.JPG
    2ded46de-dc8c-42f2-8650-0a9930dced94.JPG
    394.5 KB · Views: 63
You probably have to alter the settings to the type of sensor that's being used.


10) Control mode option

AL = Room temperature control is given priority to, the floor temperature controls the function of the
protection (electric heating is adopted)
In = only the room temperature control (water heating is adopted)
Ou = only the floor temperature control.
 