would you put a combi boiler on its own circuit via a fused spur? if not could someone please tell me the best way to go about it? thanks.:confused:
 
Is the supply already there.If not,spur off the ring to a spur and change the 13A fuse to a 3A.
 
Is the supply already there.If not,spur off the ring to a spur and change the 13A fuse to a 3A.

im just going through different scenarios, what if there is a feed already there, just a single 2.5mm cable? do you still do the same?
 
As prev replys,no problems with single 2.5 just check what pd rating is and make sure you use a 3a fuse in your spur or it will lunch the boilers pcb if theres ever a fault.
 